Two pipe steam without f and t?
    Jamie Hall Member Posts: 26,830
    Say again? Most two pipe steam systems do not have -- nor need -- an F&T. There are a few special situations where one might be needed -- but more often than not someone put one on as a bandaid fix to cover the symptom of either a failed radiator or crossover trap or, once in a while, excess pressure.
  • retep
    In holograms lost art book he says in two pipe with a dry return you need f and t
  • retep
    Holohan
  • JUGHNE
    JUGHNE Member Posts: 11,513
    If the end of the main is vented and dripped into a wet return, below the water line, (could be right at the boiler) then no F&T needed.
    Same for the dry returns from the rad traps, could be dripped the same way with air venting.
    Is this gravity return or pumped?
  • retep
    Gravity
    Steamhead Member Posts: 18,193
    Where are you located?
    Consulting
    EBEBRATT-Ed Member Posts: 19,551
    @retep
    What is your question?
  • DanHolohan
    DanHolohan Member, Moderator, Administrator Posts: 16,686
    edited May 2019
    @retep, a two-pipe steam system is going to have some sort of vent after the radiator traps because every steam system has to get rid of its air. If it's a dry-return system, the F&T at the end of the steam main (after it feeds the radiators) stops the steam from reaching into the dry return main. If there's steam in that line, the air won't be able to get out of the radiators through the radiator traps. In lieu of the trap, some of the Dead Men used loop seals at the end of the main.
    I hope that helps, and thanks for calling me "hologram." That made me laugh out loud, which is always a nice way to begin a day.
    Retired and loving it.
    And some crossover traps...
  • Erin Holohan Haskell
    Erin Holohan Haskell Member, Moderator, Administrator Posts: 2,362
    I've been thinking about adding a Holohan hologram to the website. ;)
    President
    HeatingHelp.com
  • retep
    Can't take credit for hologram I think spell check did it thanks for the help conflicting info had me wondering
  • DanHolohan
    My pleasure all around! Thanks.