Heat Loss Calculations

Options
24

Comments

  • SuperJ
    SuperJ Member Posts: 609
    edited April 2019
    Options

    @superj in that case, could the balancing problems be solved by slowing the venting on the closest radiators?


    I'll leave it to the steam experts though, I'm not a steam guy.

    https://heatinghelp.com/systems-help-center/rethinking-trvs-for-steam-systems/
  • foresthillsjd
    foresthillsjd Member Posts: 114
    Options
  • JUGHNE
    JUGHNE Member Posts: 11,061
    Options
    It is possible the date code in in the number under the lower bar code. It is at least 2002 or newer.

    Someone here can probably decipher the DOB.

    How many burners or sections do you have?
  • Jamie Hall
    Jamie Hall Member Posts: 23,289
    Options
    Balancing on one pipe steam isn't that hard -- and doesn't involve changing radiators around, which I wouldn't recommend unless you have some other very good reason for doing it.

    There are two steps to it, though -- the first step is to make sure that the main venting is really adequate. If you haven't done that, you are pretty well doomed. Once you have that, though, the rest is easy enough, if a little tedious. You need less heat in a room? Slower vent. Slow things down, though, as much as you can before you start thinking about maybe putting a faster vent where you need more heat.

    On steam boiler size: Steam boilers are not sized by the building heat loss, but rather by the installed radiation (if you were building new, you'd match the radiation to the space, then the boiler to the radiation -- but you're not).
    Br. Jamie, osb
    Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England
    foresthillsjd
  • Jamie Hall
    Jamie Hall Member Posts: 23,289
    Options

    @superj in that case, could the balancing problems be solved by slowing the venting on the closest radiators?

    Yes. But get the main venting correct first.
    Br. Jamie, osb
    Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England
    foresthillsjd
  • mikeg2015
    mikeg2015 Member Posts: 1,194
    Options

    @superj in that case, could the balancing problems be solved by slowing the venting on the closest radiators?

    Balancing starts with venting the main very fast in proportion to the radiators. Then venting based on radiator size, but using small slow vents. You want to heat evenly. I’m starting to believe that anything larger than a Gorton or MoM 5 for a radiator with EDR under 80 is just a crutch for too little main venting unles your laterals or risers are very short or the boiler is oversized.

    I underfired my boiler to a point where output it was just slightly smaller than the total radiation, so no pickup. No change in balance.
    foresthillsjd
  • ChrisJ
    ChrisJ Member Posts: 15,677
    Options
    If I was installing a steam system from scratch I would slightly oversize my radiation for each room and then size the boiler with a 10-15% pickup factor.

    A properly sized system is much easier to control and will result in less fuel usage and greater comfort.

    I reduced my boiler size by 25,000 btu/h and there no was doubt the system's behavior improved even with an outdoor reset.

    Single pipe quasi-vapor system. Typical operating pressure 0.14 - 0.43 oz. EcoSteam ES-20 Advanced Control for Residential Steam boilers. Rectorseal Steamaster water treatment
    foresthillsjd
  • ethicalpaul
    ethicalpaul Member Posts: 5,702
    Options

    On steam boiler size: Steam boilers are not sized by the building heat loss, but rather by the installed radiation (if you were building new, you'd match the radiation to the space, then the boiler to the radiation -- but you're not).

    Isn't she though? It's down to the studs, she did a heat loss calculation on each room (presumably using the the new insulation (and maybe windows) that she is likely installing, then ordered radiators to match.

    True, the boiler would then be really oversized, but that's nothing new to anyone here, and if the existing radiation is too large (now very likely), slowing them down with small vents would have a similar effect on the system as having smaller radiators would. No?
    NJ Steam Homeowner. See my sight glass boiler videos: https://bit.ly/3sZW1el
    foresthillsjd
  • PMJ
    PMJ Member Posts: 1,265
    Options
    Ah, the endless debate over the size of the hardware.

    The focus should be on the control to produce and deliver an amount of steam per hour that matches the current demand for heat. How big radiators are in the rooms makes no difference to the project if all there is for them to condense is the correct amount. How partially full the radiators get in condensing that steam makes no difference unless they are too small. The only place you go wrong is if the radiation in the room is too small and even a full radiator can't condense enough steam to meet the demand. Extra radiation hurts nothing if you control the amount of steam produced. Can't overshoot if there isn't the steam to overshoot with... no matter how big the radiator.
    1926 1000EDR Mouat 2 pipe vapor system,1957 Bryant Boiler 463,000 BTU input, Natural vacuum operation with single solenoid vent, Custom PLC control
    foresthillsjd
  • ChrisJ
    ChrisJ Member Posts: 15,677
    Options
    PMJ said:

    Ah, the endless debate over the size of the hardware.



    The focus should be on the control to produce and deliver an amount of steam per hour that matches the current demand for heat. How big radiators are in the rooms makes no difference to the project if all there is for them to condense is the correct amount. How partially full the radiators get in condensing that steam makes no difference unless they are too small. The only place you go wrong is if the radiation in the room is too small and even a full radiator can't condense enough steam to meet the demand. Extra radiation hurts nothing if you control the amount of steam produced. Can't overshoot if there isn't the steam to overshoot with... no matter how big the radiator.

    Ok,
    You go ahead and get them a control to do that and let us know when it's on the market.

    Single pipe quasi-vapor system. Typical operating pressure 0.14 - 0.43 oz. EcoSteam ES-20 Advanced Control for Residential Steam boilers. Rectorseal Steamaster water treatment
  • PMJ
    PMJ Member Posts: 1,265
    Options
    @ChrisJ ,

    There are many levels to that. The simplest one - a very simple duty cycle timer in series with the Tstat will do wonders compared to a vaporstat on a big boiler. I recommend people start there. I really don't think I am needed for something as simple as that. Somehow because no off the shelf control exists the whole control subject gets shelved and all the focus remains on hardware changes. I find that tragic really.

    You already enjoy the benefits of a run time limiting control. A great approach isn't it.
    1926 1000EDR Mouat 2 pipe vapor system,1957 Bryant Boiler 463,000 BTU input, Natural vacuum operation with single solenoid vent, Custom PLC control
    foresthillsjd
  • ChrisJ
    ChrisJ Member Posts: 15,677
    edited April 2019
    Options
    PMJ said:

    @ChrisJ ,

    There are many levels to that. The simplest one - a very simple duty cycle timer in series with the Tstat will do wonders compared to a vaporstat on a big boiler. I recommend people start there. I really don't think I am needed for something as simple as that. Somehow because no off the shelf control exists the whole control subject gets shelved and all the focus remains on hardware changes. I find that tragic really.

    You already enjoy the benefits of a run time limiting control. A great approach isn't it.

    I tried a simple duty cycle timer, it was absolutely awful on my system. Far worse than just the thermostat alone.

    I'm very lucky to have a controller that had a huge amount of effort put into it and it works very well.

    Most do not have this luxury, including the OP.

    The OP is trying to redo their home, not engineer a boiler control.

    If I am mistaken, and the OP actually wants to take on something like this on top of everything else they are dealing with, I am sorry, my mistake.
    Single pipe quasi-vapor system. Typical operating pressure 0.14 - 0.43 oz. EcoSteam ES-20 Advanced Control for Residential Steam boilers. Rectorseal Steamaster water treatment
    foresthillsjd
  • foresthillsjd
    foresthillsjd Member Posts: 114
    Options
    Wow, I feel like I'm learning a lot about the various factors to consider when designing a steam system, and it's fascinating, but I'm still at a loss for how big size the radiators. How bad is short cycling for a system? It seems that if a boiler is designed for heat loss on a design day, short cycling is going to be happening most of the time anyway. My annual gas bill for heating is about $1140, and my boiler is grossly oversized. So, what would you guys do if you had to replace all the radiators in this system? Reminder:

    Boiler Output: 145,000 BTU/hr
    Radiators That Were Connected: 80,449 BTU/hr
    Actual Heat Loss: 46,691 BTU/hr (excludes basement, which runs on a hot water loop off the boiler, heat loss of about 10,000 BTU/hr)

    Options are to decrease, increase, or keep the radiation the same.

    And then when it comes time to replace the boiler, what size do you buy? Total radiation plus a pickup factor of 10%? 20%? 30%?

  • foresthillsjd
    foresthillsjd Member Posts: 114
    Options

    On steam boiler size: Steam boilers are not sized by the building heat loss, but rather by the installed radiation (if you were building new, you'd match the radiation to the space, then the boiler to the radiation -- but you're not).

    Isn't she though? It's down to the studs, she did a heat loss calculation on each room (presumably using the the new insulation (and maybe windows) that she is likely installing, then ordered radiators to match.

    True, the boiler would then be really oversized, but that's nothing new to anyone here, and if the existing radiation is too large (now very likely), slowing them down with small vents would have a similar effect on the system as having smaller radiators would. No?
    This is very interesting to me. Here's a hypothetical question that I'm only asking out of curiosity. Let's pretend we a baby boiler that kicks out 10,000 BTU/hr to heat one room that has a heat loss of 2,500 BTU/hr. If you graphed the temperature versus time for that room under the following situations, what would they look like?
    1. On a design day, with a radiator rated at 5,000 BTU/hr with a fast vent. This will fill fast, hold a lot of heat, and then radiate it out over time.
    2. On a design day, with a radiator rated at 5,000 BTU/hr with a slow vent. This will take a longer time to fill, but once it is filled, it the curve will look like the fast vented one once it's filled, right?
    3. On a design day, with a radiator rated at 2,500 BTU/hr with a fast vent. This will fill fast, but since it holds less heat, the boiler is going to turn off and then have to kick on again before the two options above.
    But then what does that graph look like on a mild day? On a mild day, the 5,000 radiators won't fill all the way, right? Cycling is inevitable for all three scenarios, but is it going to be significantly different between the three?

    tchack
  • PMJ
    PMJ Member Posts: 1,265
    edited April 2019
    Options
    I tried a simple duty cycle timer, it was absolutely awful on my system. Far worse than just the thermostat alone.

    I'm very lucky to have a controller that had a huge amount of effort put into it and it works very well


    Classic response here @chrisj....don't even think about trying something simple because it will be worse. Any actual control change has to be a huge effort.

    I'm not sure what timer setup you tried, but what I am talking about has easy adjustments that could move you away from straight thermostat control in such small increments you wouldn't know the difference. But somehow you jumped straight to awful! So I'm guessing we must be talking about two different things.

    Anyway, you demonstrate plainly why the conversation here will likely stay on hardware. Mark S. made a fine control as you attest and this market didn't want it. Pretty tough crowd. Surely not one that invites any control development obviously. Hmm, maybe related to why there hasn't been much? I'm pretty sure a whole bunch of money has gone into hardware changes in recent years that would have been much better spent on his control. Ecosteam really doesn't care how big the boiler or the radiation is as long as both are clearly enough. Neither do I.

    Also, it appears to me the OP is quite interested in at least thinking about all the subjects.
    1926 1000EDR Mouat 2 pipe vapor system,1957 Bryant Boiler 463,000 BTU input, Natural vacuum operation with single solenoid vent, Custom PLC control
    foresthillsjd
  • Jamie Hall
    Jamie Hall Member Posts: 23,289
    Options
    I think I should write an article..

    First, on @foresthillsjd questions revolving around the existing boiler. It is not only wildly oversized (by a factor of 2) for the connected radiation, both the radiation and the boiler are oversized for the heat loss.

    Having the radiation oversized relative to the heat loss is not uncommon. In fact, as the OP points out, even in situations where the radiation is sized closely to the design day heat loss, it will be wildly oversized most of the rest of the time. The OP's comments on the behavior of the radiation under various conditions are well thought out; it is, however, fundamentally a control problem.

    Some systems (such as a mod/con hot water system) can modulate the output of the radiation to match the space heat loss. In that scenario, the radiation is always on, and always just warm enough to counter the heat loss. This, however, is not quite as simple to do as it sounds. The problem, of course, is that the heat loss is not governed solely by outside air temperature, which is the usual controlling parameter. Other factors come into play, such as solar gain and wind load and infiltration, as well as occupancy. Therefore such a system must, in fact, be slightly over designed, to ensure that in more extreme conditions (which can be either less or significantly more heat loss) there is adequate input -- which then must be managed. More on that in a moment.

    Many types of systems cannot modulate the radiation output -- never mind the boiler (read on -- boilers are next) by varying instantaneous output. Instead, they must rely on varying the average output by having the radiation alternately heating up and cooling off. In control theory, this is referred to as pulse modulation, and there is nothing wrong with it -- properly managed. If one gets into it deeply, it can get rather complex, but in principle all that one is trying to do is to control the ratio of on time to the total time between individual on events, and to select that total time between on events so that the system performs as you want it to in other regards. Having elements in the controlled system which respond slowly to being turned on and turned off helps tremendously; one of the reasons large heavy cast iron radiators give such satisfactory results is the while they heat relatively rapidly, the cool much more slowly, evening out the heat delivery to the space while the heat source is off (in electronics, where pulse modulation is used all the time and is indeed inevitable, if the power supply is alternating current, this is done with capacitors)(one of the reasons why radiant floors of concrete can be so satisfactory is that the response times are really long -- on the order of hours to days)(piston engines are also pulse modulated machines -- only there the intensity of the on pulse is modulated, as well as the pulse frequency. The flywheel, of course, evens out the net power output).

    The trick then is to control the on and off cycles, and it must be accepted that there will be some variation in heat input to the space during the cycle -- which means there will be some variation in temperature of the space over the span of a cycle. So the objective of the exercise is to keep that variation to a minimum (suggesting a high pulse frequency -- short cycle time) while ensuring that the system works efficiently (which usually means a somewhat longer cycle time -- long enough, for instance, for the heat supply to reach all of the radiation in the building).

    There are various control devices and schemes to accomplish all of this. At the risk of sounding stone age, by far the simplest is a properly calibrated thermostat, located so that it reliably samples the space temperature. Some thermostats do better at this than others, primarily by adding into the space temperature a mechanism to compensate for the speed with which the radiation itself heats up and cools off. Some of the modern digital computer based ones can "learn" this behavior, and can do remarkably well. Some of the stone age ones, equipped with "anticipators" can do just was well, but do require an intelligent human to adjust them properly.

    More, on boiler control, in the next post...
    Br. Jamie, osb
    Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England
    foresthillsjdCanuckerethicalpaul
  • Jamie Hall
    Jamie Hall Member Posts: 23,289
    Options
    Part two...

    Now a bit on boiler control.

    First, some boilers can be modulated -- that is, the burners are designed in conjunction with the boiler so that the heat input -- and hence the heat output -- can be varied in response to some outside signal. With good engineering and good control systems, these can retain most of their combustion efficiency over a wide range -- and one of the interesting developments is that boiler manufacturers are getting better at this. I might point out that control of combustion over a wide range, while maintaining efficiency, is not simple. For hot water or hot air systems, these can be used to vary the temperature of the heat transfer medium -- for instance, by outdoor reset -- to match the load rather closely, although the match can never be exact except by accident. Hence a thermostat is still needed.

    Most boilers, however, are either on or off. Therefore, some system must be available to control the pulse modulation character of the boiler. Here the vexed question of oversize comes in. If the boiler is really seriously oversized -- say, for instance, the one @foresthillsjd is talking about -- there is something to be said for using a timer to effectively reduce the average power of the boiler. The setting of the timer must be such that the system works properly -- that is, that all the radiation can and does heat. The off time length will then be such that the average output of the boiler matches the system demand or capacity. Some systems -- notably the "Heat Timer" and related systems -- have a slightly different approach, in that they vary the on time in response to some other parameter, such as outdoor air temperature. In systems in which the boiler is more closely matched to the radiation capacity, however, equally satisfactory control can be achieved by extending the observation that in a perfectly matched system, either the delivery pressure for steam or the return water temperature, for hot water, will rise to a certain level when the boiler fires -- and stay there. For steam, then, if one notes that the pressure rises and then stays essentially constant, the match is good. If it then rises again, more steam is being produced than can be condensed -- at which point (not at some arbitrary pressure) the boiler can be shut down briefly for the radiation to catch up, and then refire. A similar scenario can be used for hot water.

    Again, a properly calibrated pressure control can do the job very simply for steam, and a similarly properly calibrated aquastat for hot water.

    Note that in both the above settings, the pressure control or aquastat is strictly a control device; there should be, as always, another independent control as a safety device.

    I hope I haven't bored anyone unduly...
    Br. Jamie, osb
    Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England
    foresthillsjdCanuckerethicalpaulvibert_c
  • ChrisJ
    ChrisJ Member Posts: 15,677
    edited April 2019
    Options
    @Jamie Hall For the average person, I don't care if they use a thermostat or a vaporstat or a low pressure pressuretrol. As long as it's a well tested and reliable device.

    For someone like @PMJ that has the ability and free time to make a better control, by all means go ahead, as long as they know what they are doing and the risks involved if the control should fail.

    Most people do not have the ability to design and prove out a control.


    @foresthillsjd If you're going to reduce the amount of radiation you have, I highly urge you to replace the boiler as well. A properly sized boiler will not only save you money in the long run, it'll run much nicer the entire time.
    Single pipe quasi-vapor system. Typical operating pressure 0.14 - 0.43 oz. EcoSteam ES-20 Advanced Control for Residential Steam boilers. Rectorseal Steamaster water treatment
    Intplm.
  • SuperJ
    SuperJ Member Posts: 609
    Options
    I think she's asking should size the boiler to the radiation or heat loss, and what pick up factor should she use.

    I'm inclined to say get close to the radiation but don't add any pickup factor since her radiation exceeds the heat loss by a good margin.

    Anecdotally it seems some people run steam boilers undersized (compared to radiation), but still have very good comfort.
    I wonder if that's because of good venting/balancing of the distribution so that all rads get some steam, even if they aren't completely utilized?

    Assuming all the rads get steam at about the same time... As long as the boiler produces enough steam to satisfy the heat loss what does it matter if the rads are oversized? Or, in other words is sizing to radiation a bandaid for poor venting and balancing?


    As far the controls discussion goes, isn't PWM basically what a current CPH based thermostat does? It basically calculates a runtime for a fixed period. It doesn't seem necessary to combine a timer and a simple thermostat when a decent honeywell thermostat basically has both function integrated nicely.
  • foresthillsjd
    foresthillsjd Member Posts: 114
    Options
    SuperJ said:


    Anecdotally it seems some people run steam boilers undersized (compared to radiation), but still have very good comfort.
    I wonder if that's because of good venting/balancing of the distribution so that all rads get some steam, even if they aren't completely utilized?

    Assuming all the rads get steam at about the same time... As long as the boiler produces enough steam to satisfy the heat loss what does it matter if the rads are oversized? Or, in other words is sizing to radiation a bandaid for poor venting and balancing?

    Yes, @superj, you hit the nail on the head. That's exactly what I was wondering, but you put it much more succinctly.
  • foresthillsjd
    foresthillsjd Member Posts: 114
    edited April 2019
    Options
    ChrisJ said:


    @foresthillsjd If you're going to reduce the amount of radiation you have, I highly urge you to replace the boiler as well. A properly sized boiler will not only save you money in the long run, it'll run much nicer the entire time.

    @ChrisJ, how much of an energy loss is this oversized boiler making? I spend about $570 (corrected to say $1140) a year on gas to heat the place, so a new boiler would have to cut the gas bill in half to make sense for me.

    However, I did just learn today that I am going to have to replace my hot water heater. It's a 75 gallon tank. That thing is like a thousand bucks, and now I'm wondering if I should just convert to a condensing boiler, hot water heat that also can supply domestic hot water. I've fallen down this rabbit hole, deep.

    rabbit hole

  • ChrisJ
    ChrisJ Member Posts: 15,677
    Options

    ChrisJ said:


    @foresthillsjd If you're going to reduce the amount of radiation you have, I highly urge you to replace the boiler as well. A properly sized boiler will not only save you money in the long run, it'll run much nicer the entire time.

    @ChrisJ, how much of an energy loss is this oversized boiler making? I spend about $570 a year on gas to heat the place, so a new boiler would have to cut the gas bill in half to make sense for me.

    However, I did just learn today that I am going to have to replace my hot water heater. It's a 75 gallon tank. That thing is like a thousand bucks, and now I'm wondering if I should just convert to a condensing boiler, hot water heat that also can supply domestic hot water. I've fallen down this rabbit hole, deep.

    rabbit hole

    A steam boiler can also run an indirect for hot water.
    @Steamhead knows a lot more about those setups than I do.

    Personally I didn't do it because I didn't want my boiler hot all summer, but I can't say whether it was the best move when it comes to efficiency or not. I'm using a power vented 50gal tank heater.

    $570 a year on gas isn't much and I doubt you could cut that in half by switching boilers.
    Single pipe quasi-vapor system. Typical operating pressure 0.14 - 0.43 oz. EcoSteam ES-20 Advanced Control for Residential Steam boilers. Rectorseal Steamaster water treatment
    Canucker
  • Larry Weingarten
    Larry Weingarten Member Posts: 3,294
    Options
    Hello, 75 gallons is a big heater. I'd start by sizing the tank to your actual need. Normally it's 20 gallons for the first person and 15 for each additional person, though with low flow fixtures you can do better. Large draws like a soaking tub mess with this approach. Once you have a tank size, then look at tying it into your boiler as an indirect (which other people here can do in their sleep) or possibly going with a heat pump unit... and/or waste heat recapture, like shower drain units, which can get 60% of the "waste" heat going down the drain.
    There are lots of ways to reduce the load, so you can supply heat with a smaller, less expensive heater. I live down this rabbit hole! B)
    Yours, Larry
    ChrisJ
  • ChrisJ
    ChrisJ Member Posts: 15,677
    Options

    Hello, 75 gallons is a big heater. I'd start by sizing the tank to your actual need. Normally it's 20 gallons for the first person and 15 for each additional person, though with low flow fixtures you can do better. Large draws like a soaking tub mess with this approach. Once you have a tank size, then look at tying it into your boiler as an indirect (which other people here can do in their sleep) or possibly going with a heat pump unit... and/or waste heat recapture, like shower drain units, which can get 60% of the "waste" heat going down the drain.
    There are lots of ways to reduce the load, so you can supply heat with a smaller, less expensive heater. I live down this rabbit hole! B)
    Yours, Larry

    While I like my 50 gallon tank, we actually did survive with a 120V 20 gallon electric heater for several months. And we were a family of 3 at the time. I used that temporarily while I put gas in the house. You had to plan around it to an extent, but it wasn't that bad really.

    You know how things are now days though. Wasn't a 30 gallon gas heater considered normal years ago?
    Single pipe quasi-vapor system. Typical operating pressure 0.14 - 0.43 oz. EcoSteam ES-20 Advanced Control for Residential Steam boilers. Rectorseal Steamaster water treatment
  • PMJ
    PMJ Member Posts: 1,265
    Options

    ChrisJ said:


    @foresthillsjd If you're going to reduce the amount of radiation you have, I highly urge you to replace the boiler as well. A properly sized boiler will not only save you money in the long run, it'll run much nicer the entire time.

    @ChrisJ, how much of an energy loss is this oversized boiler making? I spend about $570 a year on gas to heat the place, so a new boiler would have to cut the gas bill in half to make sense for me.

    However, I did just learn today that I am going to have to replace my hot water heater. It's a 75 gallon tank. That thing is like a thousand bucks, and now I'm wondering if I should just convert to a condensing boiler, hot water heat that also can supply domestic hot water. I've fallen down this rabbit hole, deep.

    rabbit hole

    @foresthillsjd,

    Obviously you figured this out on your own. Math is pretty easy. There is simply no way that extra cycles from a big boiler can come close to paying for a replacement....especially one that likely won't last as long as the one you already have. I'm very glad I stuck with my big boiler 25 years ago. I'm way ahead on all fronts.

    1926 1000EDR Mouat 2 pipe vapor system,1957 Bryant Boiler 463,000 BTU input, Natural vacuum operation with single solenoid vent, Custom PLC control
    Gordy
  • coelcanth
    coelcanth Member Posts: 89
    Options
    wow $570 for the year ?
    i thought previously you had said it was double that..

    i am in queens and payed about $2000 to heat 2200sq ft last year
  • foresthillsjd
    foresthillsjd Member Posts: 114
    Options
    @coelcanth, you're right, that was a bad typo. I must have multiplied 190 by 3 instead of 6 when I wrote that. Heating only was $1140 for the year. (I basically took 6 months of gas bills during heating season and subtracted the six months of bills when I was just using it to dry clothes and heat water) It was $1500 for the entire year. What part of Queens?
  • Henry
    Henry Member Posts: 998
    Options
    Steam boiler sizing is according to the radiation installed and NOT a heat loss calculation!
  • foresthillsjd
    foresthillsjd Member Posts: 114
    edited April 2019
    Options
    > @Henry said:
    > Steam boiler sizing is according to the radiation installed and NOT a heat loss calculation!

    Agree. I the total radiation is about 83,000, but this started because I was replacing most of the radiation and when I did a heat loss, I was wondering if I should reduce the radiation.
  • PMJ
    PMJ Member Posts: 1,265
    Options
    Question: given that most early 1900's homes have much excess radiation installed (as in radiation that was never expected to be run full anyway); sizing to that will result in pretty big boilers relative to the actual design day demand won't it?

    My radiation installed in 1926 doesn't need to be 1/2 full continuously to heat just fine at -20F. I don't think the boiler is really that much over being sized for that and needs to run about 1/2 the total time to get that heating done at -20F. Maybe this is why we have so many big boilers? If you size boilers to be capable of filling radiators that never need to be close to full to get the heating done anyway they will be...big.

    Once you are getting steam to the radiators I don't think it matters how big they are as long as the boiler is big enough to heat the place. You only use as much of the radiator as is needed. Extra beyond that is extra. But if the boiler is easily big enough to cover the total heat loss that extra radiation isn't hurting anything. It doesn't somehow make the boiler too small. The only pipes that must heat up are those from the boiler to the rads.
    1926 1000EDR Mouat 2 pipe vapor system,1957 Bryant Boiler 463,000 BTU input, Natural vacuum operation with single solenoid vent, Custom PLC control
    Gordyforesthillsjdethicalpaul
  • Gordy
    Gordy Member Posts: 9,546
    edited April 2019
    Options
    Question:

    Why does a steam boiler “have” to be sized to existing radiation? Especially if it is over sized?

    Who cares if the radiator is full, or half full, or any other level of fill of the steam radiator if the quantity of generated steam heats the load?

    Really steam, and hot waters ability to modulate to load isn’t that far apart other than at the boiler. With all things equal using a ci fixed output water based boiler there is the difference of temperature of the medium to heat the rad. Say 180 for water, and 212 for steam.

    foresthillsjd
  • Jamie Hall
    Jamie Hall Member Posts: 23,289
    Options
    Pay very close attention to @PMJ 's excellent point:"Once you are getting steam to the radiators...". That is really the fundamental key to the whole thing. I would at least partly agree that if your system can and does do that, and that the radiation is getting the steam it needs, you're good to go. Some systems -- like the one in the main place I care for -- need all of the installed radiation to handle the heat loss at and below the design day temperatures -- which we do get. Many systems where there have been extensive upgrading to the envelope don't.

    But -- @PMJ 's comment is the joker in the deck. There are many variables involved here for a steam system (hot water, by comparison, is easy!): the size and length of the steam mains and risers, the way they are (or aren't) insulated, the physical arrangement of pipes and pipe junctions -- and of course the perennial favourite, venting (application of a variable vacuum comes under that heading, in my mind). The length of time between firing cycles comes into play, too. Each system will be different -- but the conservative approach of sizing the boiler output to the radiation demand with a safety factor is much less sensitive to such variations; even a system where the layout and execution out in the dark corners is, perhaps, less than optimal will work well -- or can be made to, with the major interventions being with regard to venting.
    Br. Jamie, osb
    Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England
    foresthillsjd
  • foresthillsjd
    foresthillsjd Member Posts: 114
    Options
    PMJ said:



    Once you are getting steam to the radiators I don't think it matters how big they are as long as the boiler is big enough to heat the place. You only use as much of the radiator as is needed. Extra beyond that is extra. But if the boiler is easily big enough to cover the total heat loss that extra radiation isn't hurting anything. It doesn't somehow make the boiler too small. The only pipes that must heat up are those from the boiler to the rads.

    So there's a nuance here that I want to pick at. I understand that if your goal is to heat the place, it doesn't matter how oversized the radiators are if the boiler is capable of handling the heat load. But IF the boiler is massively oversized for the heat load, would you be better off having radiators oversized for the heat loss as well, because then you would have less cycling? The boiler would get to run for a longer time to fill the radiator and then slowly cool. If the radiators were sized to match the heat loss, the boiler would be cycling more frequently for shorter intervals.
  • ChrisJ
    ChrisJ Member Posts: 15,677
    Options

    PMJ said:



    Once you are getting steam to the radiators I don't think it matters how big they are as long as the boiler is big enough to heat the place. You only use as much of the radiator as is needed. Extra beyond that is extra. But if the boiler is easily big enough to cover the total heat loss that extra radiation isn't hurting anything. It doesn't somehow make the boiler too small. The only pipes that must heat up are those from the boiler to the rads.

    So there's a nuance here that I want to pick at. I understand that if your goal is to heat the place, it doesn't matter how oversized the radiators are if the boiler is capable of handling the heat load. But IF the boiler is massively oversized for the heat load, would you be better off having radiators oversized for the heat loss as well, because then you would have less cycling? The boiler would get to run for a longer time to fill the radiator and then slowly cool. If the radiators were sized to match the heat loss, the boiler would be cycling more frequently for shorter intervals.
    I disagree with sizing a boiler to the radiation, but most here disagree with me, so there's that.

    An undersized steam boiler is difficult to balance, but if you take your time, it does seem possible. Of course, you should proceed at your own risk, knowing that it will be difficult.

    In my experience, oversized radiation with a matched boiler will cause overheating of the home and is difficult to control with just a thermostat. Meaning with a digital thermostat for example, it will overshoot by a degree or two, and then stay off too long and then not heat enough the next cycle, and then overshoot again. Rinse and repeat.

    My own system, I have 392 sqft of radiation in a 1600sqft house and I have a 104,000 btu/h output boiler rated for 325sqft assuming a 33% pickup factor.
    Single pipe quasi-vapor system. Typical operating pressure 0.14 - 0.43 oz. EcoSteam ES-20 Advanced Control for Residential Steam boilers. Rectorseal Steamaster water treatment
    SuperJ
  • PMJ
    PMJ Member Posts: 1,265
    Options

    PMJ said:



    Once you are getting steam to the radiators I don't think it matters how big they are as long as the boiler is big enough to heat the place. You only use as much of the radiator as is needed. Extra beyond that is extra. But if the boiler is easily big enough to cover the total heat loss that extra radiation isn't hurting anything. It doesn't somehow make the boiler too small. The only pipes that must heat up are those from the boiler to the rads.

    So there's a nuance here that I want to pick at. I understand that if your goal is to heat the place, it doesn't matter how oversized the radiators are if the boiler is capable of handling the heat load. But IF the boiler is massively oversized for the heat load, would you be better off having radiators oversized for the heat loss as well, because then you would have less cycling? The boiler would get to run for a longer time to fill the radiator and then slowly cool. If the radiators were sized to match the heat loss, the boiler would be cycling more frequently for shorter intervals.
    I think you are always better off with radiators oversized for the the heat loss. This is the only way to allow for operation with ultra low pressure because radiators never need to fill. This is the way these systems were originally designed for operation with continuous fire and is why we now have so many oversized boilers installed. The original boiler could never run at 100% capacity and have any control. The new boiler replaced at the same size always runs at 100%.
    1926 1000EDR Mouat 2 pipe vapor system,1957 Bryant Boiler 463,000 BTU input, Natural vacuum operation with single solenoid vent, Custom PLC control
    ethicalpaul
  • ethicalpaul
    ethicalpaul Member Posts: 5,702
    Options
    So one of the main tenets to always size the boiler to the installed radiation is questionable, I'm happy to hear it. It's another weapon to use against oversized boilers.
    NJ Steam Homeowner. See my sight glass boiler videos: https://bit.ly/3sZW1el
  • ChrisJ
    ChrisJ Member Posts: 15,677
    Options
    I'd love to see the original operating instructions to a coal boiler. Something like an Ideal Redflash
    Single pipe quasi-vapor system. Typical operating pressure 0.14 - 0.43 oz. EcoSteam ES-20 Advanced Control for Residential Steam boilers. Rectorseal Steamaster water treatment
    ethicalpaul
  • SuperJ
    SuperJ Member Posts: 609
    edited April 2019
    Options
    ChrisJ said:


    An undersized steam boiler is difficult to balance, but if you take your time, it does seem possible. Of course, you should proceed at your own risk, knowing that it will be difficult.

    In my experience, oversized radiation with a matched boiler will cause overheating of the home and is difficult to control with just a thermostat. Meaning with a digital thermostat for example, it will overshoot by a degree or two, and then stay off too long and then not heat enough the next cycle, and then overshoot again. Rinse and repeat.

    My own system, I have 392 sqft of radiation in a 1600sqft house and I have a 104,000 btu/h output boiler rated for 325sqft assuming a 33% pickup factor.


    @ChrisJ thanks for posting your example. I think it's very pertinent.

    @foresthillsjd If you have confidence in your distribution and venting, and the rads are similarly oversized to the heat loss on a room by room basis, it seems that tightening up the boiler sizing closer to the heat loss (maybe 130% of heat loss) would be the way to go. The exact size would be best determined by a steam pro who could examine your system in person and determine how aggressive you can be in tightening up the sizing. In the later TRV article I posted earlier, the author mentioned he has gotten pretty good at drawing a balance between sizing to the heat loss and radiation.

    The extreme example would be a boiler sized to the heat loss heating a single massively oversized radiator. If the rad was oversized substantially it wouldn't matter since it would still condense all the steam (and release the BTU's to the space). As you add more rads it becomes more sensitive to distribution anomalies. But venting your distribution properly makes a complicated system behave more like the one rad scenario where all the rads get hot simultaneously even if they aren't saturated with steam. One rad may be more likely to become hotter than the other if it's easier for the steam to get to some rads, think long, uninsulated, exterior walls, undersized piping.
  • Jamie Hall
    Jamie Hall Member Posts: 23,289
    Options
    If you have perfectly even distribution, and if you have the radiation sized accurately to the heat loss, then I would agree that you can probably get away with a boiler sized to the heat loss plus a factor to get steam to the radiation which factor, if the pipes are short and well insulated, can be rather small.

    If

    You can then control the system to give just enough run time to get just enough steam to the radiators to get them just warm enough to counter the space heat loss on any given day. I'll leave the control philosophy to others -- but there are many possibilities.

    Otherwise... the loss in efficiency from having a boiler correctly sized to the radiation so that, at maximum load, all the radiation gets hot and stays that way until the heating call ends is not that large; a few percent, perhaps. To the perfectionist, of course, this is not good. To the average client, and to the tradesperson who designs, specifies, and installs the system, maybe this isn't so bad. The client wants to be warm -- and to be able to warm up (people will set the thermostat back, or the power may go off...) and the last thing the tradesperson wants is to be called at oh dark hundred and 10 below with snow by a client who has a cold house.
    Br. Jamie, osb
    Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England
  • PMJ
    PMJ Member Posts: 1,265
    Options

    If you have perfectly even distribution, and if you have the radiation sized accurately to the heat loss, then I would agree that you can probably get away with a boiler sized to the heat loss plus a factor to get steam to the radiation which factor, if the pipes are short and well insulated, can be rather small.

    If

    You can then control the system to give just enough run time to get just enough steam to the radiators to get them just warm enough to counter the space heat loss on any given day. I'll leave the control philosophy to others -- but there are many possibilities.

    Otherwise... the loss in efficiency from having a boiler correctly sized to the radiation so that, at maximum load, all the radiation gets hot and stays that way until the heating call ends is not that large; a few percent, perhaps. To the perfectionist, of course, this is not good. To the average client, and to the tradesperson who designs, specifies, and installs the system, maybe this isn't so bad. The client wants to be warm -- and to be able to warm up (people will set the thermostat back, or the power may go off...) and the last thing the tradesperson wants is to be called at oh dark hundred and 10 below with snow by a client who has a cold house.

    As you already know, I believe in extra boiler anyway. I like to be able to cold start faster, and taking advantage of natural vacuum requires significant off time pauses - even on design day. And my abilities with special controls allow me to operate without temperature swings and pressure.

    Having said that, what I have found in my own original 1926 installation is that installed radiation is well past what is really needed to cover the heat loss even at record cold. I believe this to have been the design for control reasons. A partially filled radiator is adjustable, a filled one not so much.

    So I do agree with those like @ChrisJ who argue for using less pickup factor and therefore installing smaller boilers in conventional control settings. From the point of just what is required to heat, sizing to include condensing in all the radiation at once plus a pickup factor will result in a very large boiler relative to worst case actual demand.

    I also think measuring % burn time of total time at design day cold demand will give a pretty good indication of where your boiler is vs heat load. Mine is at 50% at record cold. It is sized pretty well to the radiation - which even at record cold doesn't need to be very full to cover the demand...maybe 1/2 or so.

    One other thing to consider. When we speak of how full the radiation is we must also talk about what % of the total time it is that full. Average fill level might be a better way. In the original design the fill level was quite constant as it was quite impossible to change it quickly anyway. With fixed 100% fire intermittent boilers the fill level required gets higher the fewer cycles there are. If you aren't going to fire very often you must fill the radiators fuller each time to get the average required. I chose to find a control that would be more like the continuous fire result at the rads. Obviously the fill level required to meet the demand is the smallest when it is constant. It only took me 2.5-3 cycles per hour with burns of 8-10 minutes each +/- to get rads that fluctuate between 180 down to 140 F along the top from the end of one burn to the start of the next. Calls for heat get longer and longer (into hours) the colder it gets. I really didn't like the cycles of boiling hot full rads with then long waits while they cooled all the way down. My heat is much more even now with vacuum continuing some flow going between the burns.
    1926 1000EDR Mouat 2 pipe vapor system,1957 Bryant Boiler 463,000 BTU input, Natural vacuum operation with single solenoid vent, Custom PLC control