1936 Two Pipe Steam System - Stamford CT
YE_79
Member Posts: 2
Hello, looking for recommendations for a reliable and trustworthy mechanic/technician/diagnostician in the area for a 1935/36 two pipe steam system. Just closed on the home and am undertaking a significant renovation. Any steam-heads in this neck of the woods? Thank you.
While you wait, you could post some pictures.
From what you might learn here you are prepared to vet any potential steam contractors.0 -
Where is your neck of the woods?—NBC
Edit-now I see!!- Connecticut0 -
Step one would be to order the book "We Got Steam Heat" -- a good place to start.Br. Jamie, osb
I will try to post some pics, but thought you all might get a kick out of the attached/uploaded original specs for the heating system. We were fortunate enough to find the original 1935 architectural drawings and specifications during clean-out and demo. Any ideas for technicians in the area? Fairfield County, Ct.0
Ah. Originally a Webster vapour system, I see. A very fine steam system. Unfortunately, also very subject to knuckleheads.
You might try Charles Garrity ( @Charlie from wmass ) -- I think he has been known to get that far. One of the best.
In the meantime, make sure that the system cutout pressure is less than a pound -- probably more like 8 ounces. You'll need a vapourstat to do that.Br. Jamie, osb
Nice piece of history you have there.
@Jamie Hall I was just working on a Webster system yesterday I Ascutney VT. They are quite particular about keeping the pressure on the low side.Cost is what you spend , value is what you get.
cell # 413-841-6726
Anyone notice the boiler size in the spec compared to the radiation?1926 1000EDR Mouat 2 pipe vapor system,1957 Bryant Boiler 463,000 BTU input, Natural vacuum operation with single solenoid vent, Custom PLC control0
I did, in fact. It looks like when you factor in another 33% piping and pick-up to the Radiation the boiler is still about 25% larger than the connected radiation and this was an oil system so coal wasn't a factor.PMJ said:Anyone notice the boiler size in the spec compared to the radiation?
Although the contract does say the Contractor is obligated to verify all measurements/sizes and that the specifications are a general guide. Can't say what was actually installed?0 -
Remember the boiler rating may not have had a pickup factor like we do now. Also they were factoring in for the domestic water production with the taco sidearm.Cost is what you spend , value is what you get.
cell # 413-841-6726
Weren't the controls actually more sophisticated than a simple pressure stop? As discussed before it doesn't take a lot more control than that to turn extra boiler into an asset.1926 1000EDR Mouat 2 pipe vapor system,1957 Bryant Boiler 463,000 BTU input, Natural vacuum operation with single solenoid vent, Custom PLC control0