exposed pipe support or draft inducer fan?
paulmars
Member Posts: 103
in Oil Heating
I think a draft inducer TJERNLUND DJ3 or D3 would be better, but might go with pic 1 and 2 if i can tie this up strong against 200mph winds. thoughts?
pics https://imgur.com/a/iUpwUfF
and
https://imgur.com/a/dTC6B2q
and
Ridiculous
and not legalSTEVEusaPA said:Ridiculous
Any thoughts about the addition of a draft inducer on a direct vent system with pressure over the fire and the breech being the same without any blockage?0
Why? What's wrong with venting it the way the manual recommends? I certainly wouldn't add a draught inducer -- it will, almost inevitably, do evil things to the draught over the fire and the combustion.Br. Jamie, osb
LOL. Perhaps you should consider just using listed venting installed to the listing? Where is this? In the US, you cannot use single walled pipe out through the building. It must be a 'vent' or 'chimney'. You are not allowed to vent downhill-rise 1/4" per LF The listed termination should be fine. If you have a 200 mph wind just understand when the vent ends up in the yard, it is an insurable loss. If you have a 200 mph wind, you should have the furnace shut down and you should be in another State.
Those draft inducers create positive vent pressure. Therefore, the vent pipe would have to be listed for positive vent pressure. A mfr. can call them "inducers" instead of power venters but check the draft pressure downstream and it will be positive WRT the CAZ.0