Replacing 120k btu LP Carrier 5 ton AC unit looking for the best option
Nland
Member Posts: 5
House has very high ceiling this is for the lower unit i am thinking dual fuel
i was looking into the 20 seer trane but then people are telling me anything over 16 seer when they have issue's it can be pricey. A few people have suggested Bosch? we are in the DC metro area so it does get cold but no that cold the ac has always worked fine the heat is the issue any thoughts
1
Need to know what type of equipment you have.
Furnace with an AC coil??
Packaged unit??
Heat Pump ??0 -
Its currently a carrier 2006 92% LP with a 5 ton Ac ive been told its the worst model Carrier has ever sold. the 2ndairy manifold was replaced 3 years ago there was a class action suit against carrier. now it starts up but once it reaches tempature if you increase it goes throught the lock out shut it down wait for 10 minutes usually it will fire up
The house size is about 4,686
Total SFLA (Includes Fin. Bsmt) 7,136 sq feet has a 4 ton LP in the attic0 -
Just a WAG that the attic furnace is 80-100 input, then your numbers fit into the back of the napkin heat loss/gain calculations. (the basement loss/gain counts only a fraction of the rest). That napkin form guarantees the installer will always CYA for sizing. I know, having done it myself....always oversized!
Your problem furnace; does the burner run constantly until T-stat shuts down....or does it cycle on high limit before reaching set temp?
Then when you turn T-stat up the next burn cycle will again trip the high limit....only you notice it now.
Often there is a problem with duct work sizing, especially return ducting. 5 ton AC should have 300 square inches....about 30 X 10 supply. The return should be about 400 sq inches, 40 x 10 ductwork.
Great question i will check to see if its shutting down prior to reaching temp yesterday i shut it off for 10 minutes then bumped it to 71 from 66 to 71 it did fine its still intermittent .
Are zones similar to dampers because the basement is completetly finished the only place to add a damper the main trunk directly above the Furnace0 -
Now i am being told that the current system is starving for air and i need to raise the new unit on a box so the that the 2 returns bring in more air
What size is the air filter for this now?0
- 87.1K THE MAIN WALL
- 58 Biomass
- 113 Chimneys & Flues
- 110 Geothermal
- 161 Indoor-Air Quality
- 996 Plumbing
- 391 Solar
- 55 Water Quality
