Main vent install with saddle clamp??!

Options
2»

Comments

  • ewalls29
    ewalls29 Member Posts: 26
    Options
    excellent. Thanks Gary.
  • ethicalpaul
    ethicalpaul Member Posts: 5,704
    edited December 2018
    Options
    Maybe. You should get a 0-3psi gauge because your gauge that goes to 30psi is much too large of a scale to be meaningful. You want to be able to see the actual pressure at various times while your boiler is...boiling.

    Code does require you to have a gauge that can display twice the pressure of your pressure relief valve, I've been told, but no police have come to my house yet to arrest me for swapping mine out.

    Is your main vent getting to see any steam yet?
    NJ Steam Homeowner. See my sight glass boiler videos: https://bit.ly/3sZW1el
    ewalls29
  • ewalls29
    ewalls29 Member Posts: 26
    Options
    @ethicalpaul main vent now gets really hot after adjusting the pressuretrol. Everything seems to be working up to par, just need to adjust some rad air vents and i'm ready for 'old man winter'. Thanks for your suggestions!
    ethicalpaul
  • ethicalpaul
    ethicalpaul Member Posts: 5,704
    Options
    OK excellent, so the Big Mouth is closing, sounds like!
    NJ Steam Homeowner. See my sight glass boiler videos: https://bit.ly/3sZW1el
  • ewalls29
    ewalls29 Member Posts: 26
    Options
    QUICK UPDATE: just checked Dec 2017 readings vs this year and have already used 15% less gas to heat my furnace! Running like a well oiled machine. Not bad for having installed the saddle mid dec (17th)!
    ethicalpaul