Main vent install with saddle clamp??!
Comments
-
excellent. Thanks Gary.0
-
Maybe. You should get a 0-3psi gauge because your gauge that goes to 30psi is much too large of a scale to be meaningful. You want to be able to see the actual pressure at various times while your boiler is...boiling.
Code does require you to have a gauge that can display twice the pressure of your pressure relief valve, I've been told, but no police have come to my house yet to arrest me for swapping mine out.
Is your main vent getting to see any steam yet?NJ Steam Homeowner.
Free NJ and remote steam advice: https://heatinghelp.com/find-a-contractor/detail/new-jersey-steam-help/
See my sight glass boiler videos: https://bit.ly/3sZW1el-1 -
@ethicalpaul main vent now gets really hot after adjusting the pressuretrol. Everything seems to be working up to par, just need to adjust some rad air vents and i'm ready for 'old man winter'. Thanks for your suggestions!1
-
OK excellent, so the Big Mouth is closing, sounds like!
NJ Steam Homeowner.
Free NJ and remote steam advice: https://heatinghelp.com/find-a-contractor/detail/new-jersey-steam-help/
See my sight glass boiler videos: https://bit.ly/3sZW1el0 -
Categories
- All Categories
- 86.1K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 52 Biomass
- 422 Carbon Monoxide Awareness
- 88 Chimneys & Flues
- 2K Domestic Hot Water
- 5.3K Gas Heating
- 98 Geothermal
- 155 Indoor-Air Quality
- 3.4K Oil Heating
- 62 Pipe Deterioration
- 908 Plumbing
- 6K Radiant Heating
- 380 Solar
- 14.8K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements