If you’ve got it, show it off!
nicholas bonham-carter
Member Posts: 8,578
This University of Chicago chiller plant won an Architectural award.
https://cdnassets.hw.net/dims4/GG/1777320/2147483647/resize/876x>/quality/90/?url=https://cdnassets.hw.net/a8/ee/76f5493342b58d63114bdf961878/f6068b3b1d28441db9c7268894bd26d4.jpg
I wonder if one of those is a heat recovery chiller? Most of the year there’s a huge opportunity to use condenser water for reheat rather than a boiler. I worked on a hybrid heat recovery geothermal chiller with a 140T 6 stage scroll chiller. Was valved so you could use various stages for heating or cooling at the same time or Sink or Source the ground loop.
Was a really great idea, but HORRIBLE control system and mechanical engineer mucked up a bunch of little things that limited its overall performance.
Warning...never ever use a modulating end loop bypass. Use seperate variable flow pumps for the primary and secondary with an thermal storage tank as a low loss header. Would have worked perfectly that way.1 -
We will never see are facility on there
Both of their new chiller plants are impressive new glass buildings. Their steam plant is adjacent to this building and provides an extensive district steam system - I keep telling them to extend it two blocks further so my building can connect.0