Taco 404-4ex to Indirect DHW Tank TPI Thermostat
connecting to
https://file.ac/qhPkptLqjwo/Sage Zone Control Valve Panel Instruction Sheet.pdf
hot rod said:
R & C from the Sage should be 24V, do you have a meter, you can confirm that. So those two go to the two right hand connections on the TPI, that powers it up. No ground, just use the two terminals provided.
What isn't clear is the two left connections on the TPI, I think they are dry contacts, a meter would confirm that since the wiring diagram is not real clear.
If so jumper from Red on the right terminals to either left terminal, that puts you hot leg on the switch, the other left terminal gets white wire back to W on the Sage. That will send the signal back to the Sage, which in turn opens the Z-one.
The Z-one end switch after 15 seconds turns on the call to the boiler, indicator lights on the Sage confirm the Z-one has made it's end switch.
Maybe someone else here knows the TPI and IF the left two connections are a dry contact.
The fact that the wiring schematic shows either 120V or 24V on those connections makes me think it is just dry contacts that you apply power to?
www.afinalsalute.com
 This is what Hot Rod suggested.Zman said:It has to be dry. I would just wire the 2 terminals on the left of tank control to R-W on the sage.
 https://us.v-cdn.net/5021738/uploads/editor/bd/uta81667j5fz.pngCombat Veteran owned, Final Salute LLC on FaceBook & Twitter.
 www.afinalsalute.com0
            To know for sure what the left two connections are, either call the manufacturer of the control, ask if they are powered or dry contacts. Or use a multi meter and see what, if anything reads on the left two, when you put 24V one the right two connections.
 Just hook up the right side as I show, power up the control, set the temperature up to turn the control on. Either you see 24V on the left two connections, or not. If not, my drawing works fine.
 Not much more we can do from afar to help, unless someone familiar with this control pipes up.Bob "hot rod" Rohr
 Living the hydronic dream-1
            I have an email in to Taco. They are taking their time getting back with me.Combat Veteran owned, Final Salute LLC on FaceBook & Twitter.
            Taco would have to communicate with TPI, that is where the question is. Unless they have already been down this road and confirmed the operation of the TPI model or version you have.
 Usually they add schematics to their wiring guidebook when something new or different comes along, did you look there?
 I'm not sure how tech support works when control is private labeled, it varies from company to company, they might send you back to the boiler folks.
 Taco is good about monitoring this site, if they have an answer they usually share.
 Some manufacturers will ask if you have a test meter, when you call for tech support on an electronic device, if not that is about as far as the call goes Bob "hot rod" Rohr Bob "hot rod" Rohr
            Hi
 If you’re referring to No/Com terminals, they are dry. You can energize them with 120, or 24v. They are normally used for DHE pump. If you have a system pump, you can de-energize system pump using NC terminal too. I’m happy to talk to you today if this is your Sunday project and you still have questions.
 My cell is 401-261-4890
 Tech support at 401-942-8000 can answer your questions Monday morning too.Joe Mattiello
 Taco Comfort Solutions-2
            The diagrams on page 15 show a jumper form the right side terminals to the left side.
 Thanks, I have an Alpha 2 ECM that runs all four zones and does not require outside switching or power. I'm connecting a Burnham Sega valve control panal to a Burnham indirect DHW heater TPI thermostat so you would think the two would be compatible.Joe Mattiello said:Hi
 https://www.ecomfort.com/manuals/alliancesl_io_manual.pdf
 connecting to
 This is one of the suggestions from Hot Rod, if this is correct I will go with this.
 Thanks againCombat Veteran owned, Final Salute LLC on FaceBook & Twitter.
            hot rod said:Taco would have to communicate with TPI, that is where the question is. Unless they have already been down this road and confirmed the operation of the TPI model or version you have.
 It is a Burnham boiler, Burnham Sage controller and a Burnham indirect with TPI thermostat. Should be all plug and play so to speak.
 Some manufacturers will ask if you have a test meter, when you call for tech support on an electronic device, if not that is about as far as the call goes Combat Veteran owned, Final Salute LLC on FaceBook & Twitter. Combat Veteran owned, Final Salute LLC on FaceBook & Twitter.