Taco 404-4ex to Indirect DHW Tank TPI Thermostat
https://www.ecomfort.com/manuals/alliancesl_io_manual.pdf
connecting to
https://file.ac/qhPkptLqjwo/Sage Zone Control Valve Panel Instruction Sheet.pdf
hot rod said:
R & C from the Sage should be 24V, do you have a meter, you can confirm that. So those two go to the two right hand connections on the TPI, that powers it up. No ground, just use the two terminals provided.
What isn't clear is the two left connections on the TPI, I think they are dry contacts, a meter would confirm that since the wiring diagram is not real clear.
If so jumper from Red on the right terminals to either left terminal, that puts you hot leg on the switch, the other left terminal gets white wire back to W on the Sage. That will send the signal back to the Sage, which in turn opens the Z-one.
The Z-one end switch after 15 seconds turns on the call to the boiler, indicator lights on the Sage confirm the Z-one has made it's end switch.
Maybe someone else here knows the TPI and IF the left two connections are a dry contact.
The fact that the wiring schematic shows either 120V or 24V on those connections makes me think it is just dry contacts that you apply power to?
Combat Veteran owned, Final Salute LLC on FaceBook & Twitter.
www.afinalsalute.com
  • Zman
    Zman Member Posts: 7,614
    It has to be dry. I would just wire the 2 terminals on the left of tank control to R-W on the sage.
    Albert Einstein
    cnmdesign
  • cnmdesign
    cnmdesign Member Posts: 103
    This is what Hot Rod suggested.
    https://us.v-cdn.net/5021738/uploads/editor/bd/uta81667j5fz.png
  • Zman
    We are saying the same thing. His diagram is also powering the DHW controller.
    Albert Einstein
    cnmdesign
  • cnmdesign
    So I should just go ahead and wire it up like his diagram.
  • Zman
    Yes
    Albert Einstein
    cnmdesign
    hot_rod Member Posts: 27,704
    To know for sure what the left two connections are, either call the manufacturer of the control, ask if they are powered or dry contacts. Or use a multi meter and see what, if anything reads on the left two, when you put 24V one the right two connections.
    Just hook up the right side as I show, power up the control, set the temperature up to turn the control on. Either you see 24V on the left two connections, or not. If not, my drawing works fine.
    Not much more we can do from afar to help, unless someone familiar with this control pipes up.
    cnmdesign
  • cnmdesign
    I have an email in to Taco. They are taking their time getting back with me.
    Taco would have to communicate with TPI, that is where the question is. Unless they have already been down this road and confirmed the operation of the TPI model or version you have.
    Usually they add schematics to their wiring guidebook when something new or different comes along, did you look there?
    I'm not sure how tech support works when control is private labeled, it varies from company to company, they might send you back to the boiler folks.
    Taco is good about monitoring this site, if they have an answer they usually share.
    Some manufacturers will ask if you have a test meter, when you call for tech support on an electronic device, if not that is about as far as the call goes :)
    cnmdesign
  • Zman
    It is a dry contact. This is from the manual.
    Albert Einstein
    STEVEusaPAcnmdesign
  • Joe Mattiello
    Joe Mattiello Member Posts: 751
    Hi
    If you’re referring to No/Com terminals, they are dry. You can energize them with 120, or 24v. They are normally used for DHE pump. If you have a system pump, you can de-energize system pump using NC terminal too. I’m happy to talk to you today if this is your Sunday project and you still have questions.
    My cell is 401-261-4890
    Tech support at 401-942-8000 can answer your questions Monday morning too.
    Joe Mattiello
    Taco Comfort Solutions
    cnmdesignErin Holohan Haskell
  • Zman
    The left terminals on the indirect are the ones being discussed.
    Albert Einstein
    cnmdesignJoe Mattiello
  • cnmdesign
    edited November 2018
    The diagrams on page 15 show a jumper form the right side terminals to the left side.
    Hi
    Thanks, I have an Alpha 2 ECM that runs all four zones and does not require outside switching or power. I'm connecting a Burnham Sega valve control panal to a Burnham indirect DHW heater TPI thermostat so you would think the two would be compatible.
    connecting to
    This is one of the suggestions from Hot Rod, if this is correct I will go with this.
    Thanks again
  • Hot Rod's drawing is the same as the one Zman found from the manual. I think you're safe to wire it that way, jumper and all.
    cnmdesign
  • cnmdesign
    It is a Burnham boiler, Burnham Sage controller and a Burnham indirect with TPI thermostat. Should be all plug and play so to speak.
  • Joe Mattiello
    Ok, thanks. looking at the drawing, they are using the dry switch to energize the zone-valve on demand. the schematic looks like the way to go.
    Joe Mattiello
    Zmancnmdesign