Zone Heating Issues
Ni24ck
Ni24ck Member Posts: 2
I have a 3 zone system and when one of the zones calls for heat, the other zones also heat as well but the circulator pumps don’t engage. For example...If I turn thermostat on upstairs the hot water flows through both upstairs and downstairs zones and vice versa. I have 2 smart thermostats and they are both wired correctly.
  • Sounds like phantom flow.
    Is this a newly installed system? If so, call the heating contractor back.
  • Zman
    Zman Member Posts: 7,609
    That is usually caused by a lack of check valves on the zones. Pictures would help
    Albert Einstein
  • Ni24ck
    HVACNUT Member Posts: 7,452
    IFC circs on the return, upside down.
    Terrific.
    Maybe the check valves were removed.
    Take some pics from farther back to show all near boiler piping.
    hot_rod Member Posts: 27,472
    Usually the stickers are placed on the circulators when checks are installed, so the next person knows.
    Pumps on the supply, with checks will eliminate any ghost, or thermosiphon flow. Hot water can rise up inside a pipe, cooler water drops around it and caused a slow but steady ghost flow condition. Pumps on the returns don't give you that protection.
  • DZoro
    DZoro Member Posts: 1,048
    Has the system ever performed properly?
    STEVEusaPA
    The Taco IFC circs come with the IFC sticker affixed to the pump. In the box theres a small black sticker that says "check removed".
    Its quite possible they were removed though, but I doubt it.