Zone Heating Issues

Options
Ni24ck
Ni24ck Member Posts: 2
I have a 3 zone system and when one of the zones calls for heat, the other zones also heat as well but the circulator pumps don’t engage. For example...If I turn thermostat on upstairs the hot water flows through both upstairs and downstairs zones and vice versa. I have 2 smart thermostats and they are both wired correctly.

Comments

  • Alan (California Radiant) Forbes
    Options
    Sounds like phantom flow.

    Is this a newly installed system? If so, call the heating contractor back.
    8.33 lbs./gal. x 60 min./hr. x 20°ΔT = 10,000 BTU's/hour

    Two btu per sq ft for degree difference for a slab
  • Zman
    Zman Member Posts: 7,569
    Options
    That is usually caused by a lack of check valves on the zones. Pictures would help
    "If you can't explain it simply, you don't understand it well enough"
    Albert Einstein
  • Ni24ck
    Ni24ck Member Posts: 2
    Options
  • HVACNUT
    HVACNUT Member Posts: 5,835
    Options
    IFC circs on the return, upside down.
    Terrific.
    Maybe the check valves were removed.
    Take some pics from farther back to show all near boiler piping.
  • hot_rod
    hot_rod Member Posts: 22,137
    Options
    Usually the stickers are placed on the circulators when checks are installed, so the next person knows.

    Pumps on the supply, with checks will eliminate any ghost, or thermosiphon flow. Hot water can rise up inside a pipe, cooler water drops around it and caused a slow but steady ghost flow condition. Pumps on the returns don't give you that protection.
    Bob "hot rod" Rohr
    trainer for Caleffi NA
    Living the hydronic dream
  • DZoro
    DZoro Member Posts: 1,048
    Options
    Has the system ever performed properly?
    STEVEusaPA
  • HVACNUT
    HVACNUT Member Posts: 5,835
    Options
    > @hot rod said:
    > Usually the stickers are placed on the circulators when checks are installed, so the next person knows.
    >
    The Taco IFC circs come with the IFC sticker affixed to the pump. In the box theres a small black sticker that says "check removed".

    Its quite possible they were removed though, but I doubt it.