Zone Heating Issues
Ni24ck
Member Posts: 2
in Oil Heating
I have a 3 zone system and when one of the zones calls for heat, the other zones also heat as well but the circulator pumps don’t engage. For example...If I turn thermostat on upstairs the hot water flows through both upstairs and downstairs zones and vice versa. I have 2 smart thermostats and they are both wired correctly.
0
Comments
-
Sounds like phantom flow.
Is this a newly installed system? If so, call the heating contractor back.8.33 lbs./gal. x 60 min./hr. x 20°ΔT = 10,000 BTU's/hour
Two btu per sq ft for degree difference for a slab0 -
That is usually caused by a lack of check valves on the zones. Pictures would help"If you can't explain it simply, you don't understand it well enough"
Albert Einstein0 -
-
IFC circs on the return, upside down.
Terrific.
Maybe the check valves were removed.
Take some pics from farther back to show all near boiler piping.0 -
Usually the stickers are placed on the circulators when checks are installed, so the next person knows.
Pumps on the supply, with checks will eliminate any ghost, or thermosiphon flow. Hot water can rise up inside a pipe, cooler water drops around it and caused a slow but steady ghost flow condition. Pumps on the returns don't give you that protection.Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0 -
-
> @hot rod said:
> Usually the stickers are placed on the circulators when checks are installed, so the next person knows.
>
The Taco IFC circs come with the IFC sticker affixed to the pump. In the box theres a small black sticker that says "check removed".
Its quite possible they were removed though, but I doubt it.0
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements