Weil-MClain EG-55 - unknown device - hissing sound
EdwinD
EdwinD Member Posts: 159
edited October 2018 in Strictly Steam
After running my EG-55 for about an hour, I start to get a hissing sound from the device attached below. Should it behave this way. It's appears to be
a vintage piece, should it be replaced? There is only one of them and its connected to a pipe running to the boiler and the steam pipes leading to the raidators. It looks like some sort of relief device. Advice please. Thanks.
Weil-McLain EG55 2 pipe Vapor System
OP Pressure .10 -.25 oz
8-Way Boiler Water Treatment
Barnes & Jones Big Mouth Vents
    Jamie Hall Member Posts: 26,809
    That's a vent. An elderly vent. I presume it's piped to the vertical pipe a little way down, out of the picture? It's hissing because the system finally built up some pressure (this is good. by the way -- it should take time to build pressure).
    Is this one pipe steam? Only one pipe going to each radiator, and small vent on the other end of the radiator? Or two pipe -- one pipe going in (often with a valve on it) and one pipe out (often with a rather odd looking elbow fitting - a trap)?
    Are there any other such devices on the system?
  • EdwinD
    edited October 2018
    @Jamie Hall Yes, its piped to a vertical pipe that then runs horizontal to the boiler and goes vertical to horizontal ceiling mounted boiler pipe. There are no other devices of this type.
    The sytem is a 2 pipe system as shown below. Thanks!
  • Fred
    Fred Member Posts: 8,542
    What pressure is your boiler running at? That Hoffman #75 vent should stay closed and not hiss after steam hits it, unless the pressure is too high and causing the vent to open or the Vent is defective and not fully closing. Additionally and In all probability, that vent is too small for your system anyway and probably needs a larger capacity vent. How long is that main? Do you only have one main? If there is another Main, it should be vented also. Why is the boiler running for a full hour? How long does it take to steam to get to that vent? That too is a good indicator of a vent being inadequate to vent the main quickly.
    EdwinD
    Steamhead Member Posts: 18,187
    Is it on the steam pipe or return pipe?
    If the former, there needs to be one on the return pipe as well.
    Consulting
    HVACNUTEdwinD
  • BobC
    BobC Member Posts: 5,539
    I had two of those Hoffman 75 vents fain in just over two years so I would not replace it with the same vent. If that is the only main vent I would replace it with the Barnes and Jones Bigmouth vent. If it is NOT the only main vent you might have to replace all the main vents to keep the system balanced.
    The Bigmouth costs no more than the Hoffman, is much higher capacity, and is much better built - the bigmouth is usually available at Amazon. The other option would be 2ea of Gorton #1 or maid O Mist #1 using an antler, this would probably cost a bit less but be more work.
    Bob
    3PSI gauge
    EdwinD1Matthias
    Just remember if you do decide to go with the BigMouth, that it won't close against water, so if there is that possibility -- don't use it. On the failure rate of the Hoffman 75s -- I have one on one of my systems, which has been working just fine for the last almost 90 years now.
    EdwinD
  • BobC
    I think they may have changed something in the last 5 or 6 years or so because I've heard of others having problems with recent 75's.
    In any case I don't recommend them any more, better to go with Gorton, MOM, or B&J depending on the application.
    Bob
    3PSI gauge
    EdwinD
  • Dave0176
    Dave0176 Member Posts: 1,178
    I always thought the green Hoffman’s were Hot water vents??
    DL Mechanical LLC Heating, Cooling and Plumbing 732-266-5386
    NJ Master HVACR Lic# 4630
    Specializing in Steam Heating, Serving the residents of New Jersey
    https://heatinghelp.com/find-a-contractor/detail/dl-mechanical-llc
    https://m.facebook.com/DL-Mechanical-LLC-315309995326627/?ref=content_filter
    I cannot force people to spend money, I can only suggest how to spend it wisely.......
  • Fred
    edited October 2018
    The green ones were the older Hoffman 75's (for steam). Hoffman decided a few years ago to save a few pennies by not painting these vents anymore and just leave the raw copper. @BobC , I too think they did something else on the internals to save some money because they just don't seem to have the life/reliability they had 10+ years ago.
    GordoEdwinD
  • EdwinD
    edited October 2018
    @Fred After running for 1 hour below is the pressure reading -- I was testing a new Vaportstat and Pressuretrol and I just added new fill water along with 1 1/2 Steamaster tablets.
    After about 75 minutes, the pressure started to rise - see below. At about this time the #75 vent began to hiss.- not loudly - but hiss nonetheless.
    I have lmited knowledge about steam boler terms - what is a main?
  • Fred
    @EdwinD said: I have limited knowledge about steam boiler terms - what is a main?
    A main is the larger pipe that runs around the perimeter of your basement or runs in one or two directions and from which you radiator run-out pipes branch off heading to your radiators.
    Given the pressures on your gauge, I would say That Hoffman 75 vent should be replaced. It should not open after it closes and while the boiler is producing steam.
    EdwinD
  • nicholas bonham-carter
    nicholas bonham-carter Member Posts: 8,578
    edited October 2018
    A larger vent such as a Gorton #2, or a Big Mouth will let the air out faster, and reduce your firing time, saving gas. The Big Mouth is a better made vent.
    Order the collection of steam books from the store here, and you will soon know as much as you need about steam systems-sometimes more than many local pros!!—NBC
    1MatthiasNew England SteamWorksEdwinD
  • EdwinD
    @Fred Thanks! Will do a replacement on the Hoffman 75 vent.
  • EdwinD
    edited October 2018
    @Fred Oh yes, meant to say it's a one main system.
  • EdwinD
    edited October 2018
    @nicholas bonham-carter I 've decided to go with the Barnes & Jones Big Mouth Vent from Amazon. I'll let you know how it goes. And I will be ordering the collection of steam books from the store. I have truly enjoyed the experience gained in making my boiler more "cutting edge." I'm excited! Thanks again!
    SeanBeans
  • EdwinD
    Bob
    @Bob. Thanks! Just purchased the Bigmouth at Amazon. Can't wait to install it.
    I wonder why it took 75 minutes to start showing signs of pressure. Usually inadequate main vents will show a high reading in a shorter time, as the air is being squeezed out of bad vents.
    Read up on “clocking the gas meter” here and make sure your boiler is getting the required amount of gas.—NBC
    EdwinD
  • EdwinD
    @nicholas bonham-carter Will do. Thanks.
  • EdwinD
    edited October 2018
    Here's what I got:
    6.5 RPM (1/2 CF dial) x 30 = 195 CF/HR
    (tested twice)
    195 CF/HR x 1000 = 195,000 BTU/HR
    My Weil-MClain EG-55 is rated at 200 AGA Input MBH
    So it appears my boiler needs a lttle more gas - about 5,000 more BTU per hour. Am I reading this correctly? Thanks
  • EdwinD
  • EdwinD
  • Fred
    @EdwinD , Your boiler/gas supply is fine. It took 75 minutes because your boiler is properly sized to the connected radiation. Even with bad or inadequate vents, some of them are still venting and, as you noted, that Hoffman 75 was opening when steam was being produced so it also prevented any possibility to build pressure. You are good to go! Change out that Hoffman 75 for a BigMouth and enjoy the system.
    EdwinD
  • EdwinD
    edited October 2018
    @Fred. Great. I should have BigMouth tomorrow. Can't wait. Thanks!
  • EdwinD
    edited October 2019
    A year later, I added a second Big Mouth yesterday. Couldn't be happier.Thanks all.
  • BobC
    I don't see how water will drain from that setup because you have built a piped in trap.
    Bob
    3PSI gauge
  • KC_Jones
    KC_Jones Member Posts: 5,907
    Bob
    ^^^^ This, you need to re pipe that or you are going to have a problem.
    2014 Weil Mclain EG-40
  • EdwinD
    edited October 2019
    @BobC @KC_Jones Thanks for the heads up! I wasn't aware any water ran thru the vent - I figured only air passed out.. Being a steam novice, what do you recommend to correct the error?
    I'm thinking maybe something like this I found on the web:
    Thoughts appreciated.
  • SeanBeans
    SeanBeans Member Posts: 525
    @EdwinD use a shorter nipple on your riser.
    Also tighten the double-45s full 180 degrees so that the water can roll back down
    EdwinD
  • SeanBeans
    Looks like you MIGHT be able to get away with a street 90 into that existing coupling.
    Get rid of both 45s if you do that method as they will limit your height.
    I’ve found the ID on the street side of a street 90 is slightly smaller than 1/2 pipe. Which will limit your venting capabilities slightly.
    EdwinD
  • EdwinD
    edited October 2019
    @SeanBeans Thanks! I get it. See the pic I added to my original post. Sounds like this is what you're describing?
    As for adding a "shorter" nipple to the riser, I'm reluctant to remove the old (longer) one since it's been there since the house was built (1929). Unintended consequences are in the back of my mind. Generally speaking, any cautionary advice anyone care to share about removing that old nipple on the riser and replacing with a shorter nipple?
    But I agree, if I can remove that old nipple and replace with a shorter one, I will have the clearance to rotate the 45s so water can roll back down.
  • SeanBeans
    Yeah, looks like you’d have to remove that old pipe to shorten it.. maybe the street 90 will be just enough
    EdwinD
  • BobC
    Some steam will condense and your pipe will fill up with water till it blocks and air or steam from going through, at that point tou will have zero venting, Do whatever it takes to have a downhill path from the vents to that vertical pipe.
    First scrape any solidified pipe compound off the joint and then put some penetrating oil (Kroil is a good one)on the long nipple lower joint every day for several days. Then rap the joint with a hammer and that should set up a vibration that will let the penetrating oil do it's work, do this every day after applying the oil. If it still won't budge use a y\iourch to heat up that coupler. that should expand it enough to let the long nipple turn.
    Then use a shorter nipple and orient everything so water can drain from the vents to the new nipple.
    Bob
    3PSI gauge
    EdwinD
  • EdwinD
    edited October 2019
    Bob
    @BobC Thanks! I'll use your process to try and remove it. You guys are great!
  • EdwinD
    edited October 2019
    Vent configuration corrected. Let me know if you have suggestions.
    I removed the too long 90 year old nipple, by spraying the joint with paint remover. It actually worked. I noticed the old timers painted all of the dry return piping black. It's like trying to open a window that's been painted shut.
    @BobC @SeanBeans @KC_Jones Thanks again!
  • KC_Jones
    Much better!
    STEAM DOCTORethicalpaulEdwinDCanucker