Crown BWC 090 gas boiler
samber
samber Member Posts: 5
I have the above boiler that is about 11 years old. It ran fine last heating season untill I shut it down for the summer.
Unable to start the unit now? It tries to start and hangs up at "checking air pressure switch" and shuts down with E28 and b61 error codes. The blower fan is running and elec. connection to pressure switch and MCBA seem ok. Removed the pressure switch and by blowing into the inlet tube the diaphragm seems to be working. Should I replace the pressure switch or is there something else I should look for?
  • Henry
    Henry Member Posts: 998
    Call a licensed gas certified plumber. Insurance will not cover you with a DIY fix.
  • Ironman
    Ironman Member Posts: 7,857
    Why do you assume that a safety is bad when it does what it's designed to do?
    You probably have a blockage in the flue or condensate drain.
    Bob Boan
    Zman
  • samber
    Ironman: thanks for the reply. the flue is clean, the condensate drain and pump are good.
  • Ironman
    The only way to confirm that the pressure switch is functioning properly is with an accurate manometer.
    Bob Boan