Taco SR502-4 Switching Relay - Unable to Power Two Ecobee4's?
I tried researching this issue but the solution still seems somewhat unclear to me. I'm in the midst of a major renovation and have had numerous issues with both the plumber and electrician and as such am trying to solve this problem myself.
A new Taco SR502-4 Switch Relay was installed for two heating zones by the contractor. An Ecobee4 thermostat was installed in each zone by the contractor. One thermostat receives power while the other does not. I've traced the issue back to the Taco Switch Relay. On the upper left corner of the circuit board there are two connections to provide power to the "C" wire. One seems to be getting approximately 27 volts while the other connection doesn't seem to be getting any power.
Ecobee support believes that the transformer is not sufficient to power both thermostats and I need a more powerful transformer and an isolation relay. Is this correct? It just seems odd to me that the second terminal is showing no voltage as oppose to low/or insufficient voltage.
Thank you for your time and assistance and I apologize in advance for any improper terminology.
Thanks,
Pat
If I read that circuit board correctly, one side of that connector is labelled "24 vac" and the other side is labelled "Com". Common usually means a return, sometimes (not always) grounded, while 24 vac means just what it says.
To what are you connecting the return from the Ecobee which works?Br. Jamie, osb
As Jamie said, you should be showing (a nominal) 24V between those two terminals, and if you show 24V between the "24VAC" terminal and ground/metal box and appx 0V between "com" and the same place that merely indicates that the common terminal is electrically to the box. If you have an ampy clampy, measure the current on the yaller or red wire from the xfrmr. if it's anything over about ½ amp, it's nearly certainly your issue.
A 15 VA xfrmr is quite small and I have no trouble believing that it is unable power two Ecobee stats and the SR502. If it were me, I'd just replace the xfrmr with a larger one, but that would not do anything good for your warranty.
What are the Blue (24v) and Black (Com) wires connected to on the Ecobee's?
You should only need the "Com" wire connected the the "C" terminal on the thermostats. The power (24v) is already there from the Red wires "R" terminals in the relay where the thermostat wires are connected. R-W. Nothing needs to be connected to the 24v terminal.
Note: For HVAC low voltage control wiring, the power wire (24v) should be Red and Common wire should be Blue or Brown.
The thermostat wiring should be simple.
R- 24v
C- common
W- to heat heat relay (your SR502)
G- to fan relay
Y- to the A/C condenser
O,B- if it's a heatpump system2 -
you need at least a 40 va transformer for that application, maybe even a 75 va transformer, not to familiar with ecobee watt consumption check that"The bitter taste of a poor install lasts far longer than the JOY of the lowest price"0
you may need a resistor
try switching places with the blue wires on the 24vac/com termial and see if the other t-stat powers up.Winter Park, CO & Arvada, CO0
@pburke
Like he saidHVACNUT said:What are the Blue (24v) and Black (Com) wires connected to on the Ecobee's?
R- 24v
C- common
G- to fan relay
Albert Einstein0 -
Thanks for everyone's insightful replies.
So based on what I've gathered from everyone's replies and a little deductive reasoning, I ended up connecting both Blue "C" / Common wires to the "COM" terminal on the Taco's board. (Please see picture below). This seems to have fixed the issue as both Ecobee's are now powering up and currently seem to be functioning properly.
Question being:
Does anyone see any potential issues with the way I did this?
Thanks again for everyone's time,
Pat1 -
Functionally, it should work; but that xfrmr is very low power. It may not be able to provide sufficient current if e.g. both stats call at the same time. The easiest way to check would be to turn them both down so they call for heat & check the voltage at the 24VAC & COM terminals—you're looking for at least 24 volts at maximum load.0
VERY similar problem with that Taco board, actually fixed via this info however: When testing for the 24v I got .3v - nothing more ever no matter how I tested. Basic Multi-meter settings but when I hooked it all up: poof! it worked. What the hell, is there a digital switch there I'm not aware of?0
@STEVEusaPA I thought the same thing.... Poof and my gut went
15VA isn't a lot of current. Probably just enough to power the circuit board and the relays.
You can add your own 40VA transformer in place of the 15VA transformer. It is very easy to do and you would have plenty of power and it would be cheap to do.0 -
so just getting the Com connected to the W of the thermostat did the trick , and you can power your thermostat with 2 wires only?pburke said:Thanks for everyone's insightful replies.
Question being:
Pat
I have a Nest and same situation
Taco SR-503-4
did you upgrade your transformer from 24VAC 15 Va to 40Va ?
no need for the 1000ohm 1/2W resistor between the COM and thermostat?
No. The W on the thermostat goes to the W on the relay for that zone. The C wire on the Nest goes to the COM terminal on the board.
So you need a three-wire cable between the Nest and the SR504.
I wouldn't trust the resistor hookup. There are way too many electronics in the base of a Nest, and they don't like shortcuts.All Steamed Up, Inc.
Consulting0 -
Not sure if my question deserves its own thread, plus I'm referencing a post in this thread, so....
When I replaced my two-wire t-stat with an ecobee, I ran a new 5-wire thingy, and added a 40vA transformer up in the joists above the boiler. Not ideal to say the least. Now I read the above post about replacing the 15vA in the SR-504 with a 40vA. Bingo, I think! But I just went and looked- the xfromer in the 504 is MUCH smaller than the 40vA. And I few other I have also. So much so that it doesn't seem like a 40vA will fit in there as a replacement. Is there some specific model I can get that will fit? Thanks!0
- 117 Geothermal