Steam replacement
Dave0176
Dave0176 Member Posts: 1,178
Started another steam replacement today, had a new helper, my 9yo apprentice. He did a great job and he worked hard today.
Old boiler was a 18yo Pennco 1606 187,000 BTU for only 430 EDR. Piped wrong as usual.
Anyway I went in with a Weil-McLain EG-50. There is a possibility the under floor return is leaking, I put the hydro level water feeder in so we monitor the water situation.
DL Mechanical LLC Heating, Cooling and Plumbing 732-266-5386
NJ Master HVACR Lic# 4630
Specializing in Steam Heating, Serving the residents of New Jersey
https://heatinghelp.com/find-a-contractor/detail/dl-mechanical-llc
https://m.facebook.com/DL-Mechanical-LLC-315309995326627/?ref=content_filter
I cannot force people to spend money, I can only suggest how to spend it wisely.......
New England SteamWorks
    EBEBRATT-Ed Member Posts: 19,543
    The old boiler was only 81% oversized. You can see they left the two black tees from the original boiler and went with copper.
    At least you took pity on the youngster and let him use an aluminum wrench!!
    Dave0176Dave in QCA
  • Phil53
    Phil53 Member Posts: 73
    Hopefully your apprentice will develop the same passion for this work that you have. Glad you are exposing him to working with his hands besides using a controller in a video game. I think a lot more kids would be interested in the trades if they just had a little exposure. These kids aren't lazy, they just don't know anything else.
    CLambdelta TDave in QCA
  • AMservices
    AMservices Member Posts: 611
    Very nice work! Hope your boy continues to follow in your foot steps. We need all the good steam guys we can get.
    Dave0176
  • New England SteamWorks
    New England SteamWorks Member Posts: 1,529
    Very nice @Dave0176! My new apprentices have to wait 90 days before getting a uniform though...
    Service, Installation, & Restoration of Steam Heating Systems
    newenglandsteamworks.com
    Dave0176Erin Holohan Haskell
  • gerry gill
    gerry gill Member Posts: 3,083
    outstanding! teaching a solid work ethic young will make him wealthy later :) Nice looking job he is doing too!
    gwgillplumbingandheating.com
    Serving Cleveland's eastern suburbs from Cleveland Heights down to Cuyahoga Falls.
    Dave0176
  • Dave0176
    Thanks everyone he did a great job for the first time and his enthusiasm is great for this work, for now anyway, I’m hoping it lasts. Anyhow the job is complete.
    ratioErin Holohan HaskellNew England SteamWorks
  • BobC
    BobC Member Posts: 5,539
    The advantage of a young helper is they have not had time to acquire bad habits,
    That is one great install.
    Bob
    3PSI gauge
  • Shalom
    Shalom Member Posts: 165
    edited May 2018
    I hope you're explaining to him what was wrong with the old piping, rather than just "well that's the way it is". If your "apprentice" is anything like my son, he'll want to know why. (As every tech who's worked in my house finds out...)
  • delta T
    delta T Member Posts: 884
    I started when I was nine, good memories. Still going strong! Very nice install, glad to see someone teaching the next generation, and glad he's got a good teacher.
  • Dave in QCA
    Dave in QCA Member Posts: 1,806
    I also hope you are explaining to him exactly why you install the piping the way you have, and each slight change that another installer might do, and why it would not be as good.
    A PERFECT installation there and a true work of art.
    Dave in Quad Cities, America
    Weil-McLain 680 with Riello 2-stage burner, December 2012. Firing rate=375MBH Low, 690MBH Hi.
    System = Early Dunham 2-pipe Vacuo-Vapor (inlet and outlet both at bottom of radiators) Traps are Dunham #2 rebuilt w. Barnes-Jones Cage Units, Dunham-Bush 1E, Mepco 1E, and Armstrong TS-2. All valves haveTunstall orifices sized at 8 oz.
    Current connected load EDR= 1,259 sq ft, Original system EDR = 2,100 sq ft Vaporstat, 13 oz cutout, 4 oz cutin - Temp. control Tekmar 279.
    http://grandviewdavenport.com
  • gerry gill
    thats a fine looking install that no one can top. I'd put that on a canvas print and hang it in the young mans room so he can be proud of it for years to come!
    Dave0176
  • Snowmelt
    Snowmelt Member Posts: 1,457
    Instead of the brass pigtail I see you fabricated your own. Can you take a closer pic so I can show some of my coworkers. With the explanation of the clean outs.
    Great job and a fabulous looking install @Dave0176 .
    Dave0176