NEED HELP! Gas Buderus boiler
Karamf
Member Posts: 8
in Gas Heating
Hello folks,
I have a buderus boiler that's in great shape but been having issues with it all Winter.
For some reason.. randomly the heat stops working at my house. The only way to get it going again, is to reset the Emergency Switch.
Even though this method is an easy fix, it's not very convenient when i'm out of town and start worrying about the pipes bursting.
We at first thought it was the Nest Thermostat (which replacing it made it work for a week flawlessly) but not it since we're apparently back at the issue.
I've had another pair of plumbers try and figure out the issue(GEM), and they suggested next time it goes to press the relay(which was replaced a year ago). Not sure how well this method works because it's essentially just resetting the boiler similar to the emergency switch method.
It's a 2 Zone setup, Would hate to start replacing parts left and right because it could really add up fairly quickly.
I have GEM coming for the 3rd time tomorrow. My original plumber couldn't figure it out, GEM can't pinpoint the issue... any help would be great.
Thank you,
Thank you,
Can you post some pictures of the equipment when it is malfunctioning? That would be a huge help when trying to figure out what the problem is.0
Honestly, since replacing the Nest once apparently resolved the problem for week, I would try substituting a plain vanilla thermostat for the Nest -- something simple -- for a while and see if the problem crops up again.Br. Jamie, osb
when you had no heat was the boiler doing anything? Inducer motor running? Circulator running? Any action at all?0
I can't say with 100% certainty what it is without checking with a multimeter, but if I had to take a guess based on what you described and what I see in the pictures I think your problems are related to the zone valves. I have seen intermittent issues caused by the end switches having worn out contact points or the valve not opening or closing completely due to the mechanical components get gunked up or worn down.
It would be great to open up that boiler and check inside too. Sometimes a control might be showing an error code. But it's a tight squeeze to get into that boiler apparently.0 -
It’s a basic boiler, it normally is easier to diagnose.
If you don’t have a zone control ( do you?) then simply feel the lever on the zone valve, is it sliding back and forth (when it’s calling for heat)?
And, when you reset the power, does the boiler start immediately? That may mean something else
Like mentioned, maybe it’s the Nests. Do the nests have C wires?0 -
Fan sounded like it was running but that was about it. No heat until things get reset
We did that. I threw on a $40 Honeywell one and that's what I thought allowed it to run for the past week. But not it's day to day on and off situation.
We replaced a zone valve last year, another yesterday. Woke up today go no heat again... Was hoping that would be it.
Fires up, zone valves are officially new and it's still acting up. The nests do call for C wires but I did not have one. Regardless it was replaced.0 -
Can you get a nice battery operated Honeywell programmable -- one of the Vision series, perhaps, from you local big box? That will allow you to program setbacks if you like; it just doesn't know when you are there or not.
The Nest must have a C wire to function properly. I think that they allege it will work without one, but we here on the Wall have found otherwise.Br. Jamie, osb
lchmb said:
If the inducer motor (small motor on top) is running it sounds like either it tried to fire and failed or never proved on the pressure switch. Either way it sounds like your issue is at the boiler..
Next thing we're testing out now is the Pilot Gas ignition control.unclejohn said:Check the tubing to the pressure switch it gets brittle and cracks
Going to get and install tonight. We'll see what happens.
thank you all for your comments. Loving this forum!0 -
Are you located in Rhode Island? If so call the Gas Doctor 401-942-5223.0
Looks like a small space.
Do you have enough combustion air?0 -
I am, if it doesn't work out with the ignition control will do.. Who should i ask for?Tim McElwain said:Are you located in Rhode Island? If so call the Gas Doctor 401-942-5223.
Sounds good! Will check it out!Big Ed said:There will be an small hose connected to an disk like switch and an barbed fitting near the fan motor , check for cracks and clean the barb fitting passage
Seems fine, haven't had any complaints in regards to it from the 6 plumbers that have been through the house in the past 3 years. hahaSuperJ said:Looks like a small space.
Little update guys... I replaced the Furnace Intermittent Pilot and haven't had a single issue since!
Thank you all for your responses!0 -
Other item, make sure someone has cleaned burners and pilot. That could also be the source of lockout causing the need to reset power. This is the first thing we go after when intermittent lockout then the module. Also, totally agree on common with Nest. or if not enough wires we wire in a relay to isolate electronics which mess with the power stealing of a 2 wire setup on Nest. Corrected 2 of these in last week.0