Can I use Taco 400-4 1/8-Inch-NPT Float Air Hy-Vent on the return on a steam system

Options
acl10
acl10 Member Posts: 349

Can I use Taco 400-4 1/8-Inch-NPT Float Air Hy-Vent on top the return on a steam system. When I put steam vent like Gorton on the return water came out. I changed it to this taco and no water comes out. When it comes on air comes out and then when the return fills with water its shuts.

Comments

  • Ironman
    Ironman Member Posts: 7,376
    Options
    You don't vent the wet return of a steam system. The vent belongs at the end of the steam main or on the dry return.
    Bob Boan
    You can choose to do what you want, but you cannot choose the consequences.
  • acl10
    acl10 Member Posts: 349
    Options
    I did both I see that the wet return goes faster
  • Fred
    Fred Member Posts: 8,542
    Options
    AS was said, you don't vent a wet return.