Welcome! Here are the website rules, as well as some tips for using this forum.
Need to contact us? Visit https://heatinghelp.com/contact-us/.
Click here to Find a Contractor in your area.
Can I use Taco 400-4 1/8-Inch-NPT Float Air Hy-Vent on the return on a steam system
acl10
Member Posts: 349
Can I use Taco 400-4 1/8-Inch-NPT Float Air Hy-Vent on top the return on a steam system. When I put steam vent like Gorton on the return water came out. I changed it to this taco and no water comes out. When it comes on air comes out and then when the return fills with water its shuts.
0
Comments
-
You don't vent the wet return of a steam system. The vent belongs at the end of the steam main or on the dry return.Bob Boan
You can choose to do what you want, but you cannot choose the consequences.0 -
I did both I see that the wet return goes faster0
-
AS was said, you don't vent a wet return.0
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements