BTUs, WC, PSI, and pipe size
Bobbymac746
Member Posts: 6
in Gas Heating
Hello, I recently put up a new barn. When trenching, I ran 1” gas tite up to a riser at the meter as well as the barn. The distance is approximately 250’. I’m looking to buy an overhead garage heater and hire a plumber to install it all in one shot. I have a 30x48x16, so I was looking at 125,000BTU heaters, but now I’m not sure if I can provide enough BTUs.
Some of these charts say I will only get 88,000BTU while one says 1115k. If my gas meter says 5psi, do I use the bigger chart? I have no idea how to figure pressure drop. Thanks for any help.
https://www.gastite.com/downloads/pdfs/gastite_sizing_tables_natural_gas.pdf
I think you're too small my friend. Maybe upping the pressure, but you may still need the volume of a larger pipe.
Depends where you are located. On low pressure your only going to get 88,000 and maybe less that that as you have to allow for the interior piping to your heater.
If you can run high pressure you can probably do it. It would require an additional regulator outside the barn.
The reason I asked about the location is I am in MA. MA. does not allow CCST to be used on high pressure even though the mfg. says it's ok.
You will have to check with your plumber and the local gas utility0 -
I hope that’s the plate you’re looking at. As you can see 5psi. Doesn’t that mean, I get the high pressure unless I put a regulator on it (pre appliance)?
You pressure regulator will tell you what your pressure is ,not your meter. It does look like the meter is capable of 5 psi.
Most residential services are set up for <0.5 psi. some are 2 psi but that is unusual."If you can't explain it simply, you don't understand it well enough"
Albert Einstein0 -
MAOP means Maximum Allowable Operating Pressure, see https://www.elster-americanmeter.com/assets/products/products_elster_files/EAM-DS3535.pdf. A better indication of elevated pressure would be a regulator at the meter, since residential equipment runs at less than 14 in wc (≈½ psi). How 'bout a pic of the meter setting from a few paces back, showing from where it comes out of the ground to where it goes into the house?0
Here is a picture from a few feet back. Thank you all for the help. I keep seeing garage heaters for good prices on craigslist and I’d like to know it will work so I can hire someone to do this all in one shot versus having to hire someone to come tell me what I can use and then having to have them come back and hook it up.0 -
It's looking like a low pressure service to me. You'll need to know the gas pressure & the minimum input pressure of the new appliance to see if it'll work. The table tells us that if your gas pressure at the inlet to the new line is under ½ lb & you flow 88k BTUh through a run that's 250' long you'll see about ½" pressure drop. It also says that if you increase that demand to 150k BTUh you'll see about 1½" pressure drop. If you're incoming pressure is high enough, say 9", and the nameplate says minimum 5.5" and a firing rate of 150k BTUh, then 9 take away the 1½ leaves 7½, more than the min of 5.5, so the math works. If your incoming pressure is 8" and the minimum is 7" you'll run into issues at 150k, but maybe not at 88k.1
Already mentioned I wasn’t doing the job myself. Just want to buy the appropriate sized heater so I don’t have to hire someone twice ( to tell me what I can run and have to come back to install). Also no idea what safety violations you’re imagining, that is a photo of the house, there is a sleeve and it was all done by a licensed plumber when the house was built. Most of the folks here have been very helpful, not you though.0
