Sit 820 gas valve kicks on when touched
dynastyss
dynastyss Member Posts: 14
Hello!
So two times now the direct vent millivolt fireplace should have been on, thermostat on, and failed to fire. Thermocouple and thermopile are showing consistent and good voltage. The only common denominator is when I go to jiggle or touch the sit 820 gas valve it instantly roars on and works for a couple days. Rinse and repeat.
I tested and it is showing 2.4 ohms. But could it still be failing or on the way out? Any other way to test it?
Thanks
  • Bob Harper
    Bob Harper Member Posts: 1,146
    Disconnect the stat and run it off a jumper. If it fails to fully ignite the burner within 4 seconds that is considered a delayed ignition and a safety issue. Post your millivolt readings. Also, what is the static and burning inlet gas pressure and manifold pressure on high? This is most reliable valve I've ever seen.
    What make & model fireplace?
    Here are troubleshooting guides from SIT:
    http://www.gdainfo.com/Resource1049853HJDUFOS023X/Touble Shooting/SIT Millivolt Valve Troubleshooting Guide.pdf
    http://www.sitgroup.it/wp-content/uploads/2017/09/820-mV-GB.pdf
    http://rs.woodmanspartsplus.com/company_41/820 instructions.pdf
    dynastyss
  • dynastyss
    edited December 2017
    Thanks Bob. So I get 500 milli with the fireplace on and around 300 with just the pilot on.
    I just attached a photo of the valve which shows the current settings.
    It is a hearthstone luno 8160
    The odd thing is it lights up super quickly. Will work wonderfully for a few days or weeks then recently has just stopped working. Won't work until someone touches the valve and it magically works again.
  • ratio
    ratio Member Posts: 4,203
    Is it a "lay a finger on the side of thew valve" touch, or is it "grab the wires and wiggle" touch? It sounds more like a poor connection on the wiring, especially if you physically move anything—even a little. remove & reinsert the wires, or loosen & tighten the terminal screws a few times. If it's a loose\oxidized connection on the valve, that should make it go away, at least for some time.
    dynastyss
    Jamie Hall Member Posts: 27,010
    If it's lay a finger type stuff, I'd bet on a bad ground. Either way, the first thing I'm looking for here is a weak connection. It may look good, but it may not be good.
    dynastyss
  • dynastyss
    It is in fact more lay finger on it material. I unplugged all the leads on the th, tp, th/tp side when testing the ohms. I didn't even realize there is a ground. What would be a good way to clean that up?
    Thanks
    The first place I would look is for the grounding of the whole thing -- which includes the gas valve -- to the switchboard in your house. There should be, somewhere, a solid neutral wire going to the switchboard (it should be a white wire) and there should also be a solid ground (which should be green). If there is no 110 volts it still needs a ground -- the green wire -- but not the white. It may not have one.
    dynastyss
  • Bob Harper
    The center terminal, TP, is the ground. Make sure all the terminals are intact by wiggling each. Note there is another set of spade connectors 90 degrees below the visible ones. Look up under the operating head and you'll see those male spade connections.
    dynastyss
  • BobC
    BobC Member Posts: 5,551
    Also make sure that knob is actually in it's detent, it may just be on the edge.
    Bob
    3PSI gauge
  • Toecheddar
    Toecheddar Member Posts: 1
    Hey there - bumping this thread. I know it's old, but I was interested to find this thread. I'm having exactly the same issue. SIT 820 propane valve. I've had a couple of years worth of issues with it sticking. Just ordered a replacement, but mine was doing the same thing OP described - when you'd push the terminal block, the valve would open. You can bridge the stat terminals with a wire, and the valve won't come on, but when you press the terminal block backwards just a little, it will open and the fireplace will light.
    Anyway, a strange failure mode.