Hello!
So two times now the direct vent millivolt fireplace should have been on, thermostat on, and failed to fire. Thermocouple and thermopile are showing consistent and good voltage. The only common denominator is when I go to jiggle or touch the sit 820 gas valve it instantly roars on and works for a couple days. Rinse and repeat.
I tested and it is showing 2.4 ohms. But could it still be failing or on the way out? Any other way to test it?
Thanks
So two times now the direct vent millivolt fireplace should have been on, thermostat on, and failed to fire. Thermocouple and thermopile are showing consistent and good voltage. The only common denominator is when I go to jiggle or touch the sit 820 gas valve it instantly roars on and works for a couple days. Rinse and repeat.
I tested and it is showing 2.4 ohms. But could it still be failing or on the way out? Any other way to test it?
Thanks
0
Comments
-
Disconnect the stat and run it off a jumper. If it fails to fully ignite the burner within 4 seconds that is considered a delayed ignition and a safety issue. Post your millivolt readings. Also, what is the static and burning inlet gas pressure and manifold pressure on high? This is most reliable valve I've ever seen.
What make & model fireplace?
Here are troubleshooting guides from SIT:
http://www.gdainfo.com/Resource1049853HJDUFOS023X/Touble Shooting/SIT Millivolt Valve Troubleshooting Guide.pdf
http://www.sitgroup.it/wp-content/uploads/2017/09/820-mV-GB.pdf
http://rs.woodmanspartsplus.com/company_41/820 instructions.pdf1 -
> @Bob Harper said:
> Disconnect the stat and run it off a jumper. If it fails to fully ignite the burner within 4 seconds that is considered a delayed ignition and a safety issue. Post your millivolt readings. Also, what is the static and burning inlet gas pressure and manifold pressure on high? This is most reliable valve I've ever seen.
> What make & model fireplace?
> Here are troubleshooting guides from SIT:
> http://www.gdainfo.com/Resource1049853HJDUFOS023X/Touble Shooting/SIT Millivolt Valve Troubleshooting Guide.pdf
> http://www.sitgroup.it/wp-content/uploads/2017/09/820-mV-GB.pdf
> http://rs.woodmanspartsplus.com/company_41/820 instructions.pdf
Thanks Bob. So I get 500 milli with the fireplace on and around 300 with just the pilot on.
I just attached a photo of the valve which shows the current settings.
It is a hearthstone luno 8160
The odd thing is it lights up super quickly. Will work wonderfully for a few days or weeks then recently has just stopped working. Won't work until someone touches the valve and it magically works again.0 -
Is it a "lay a finger on the side of thew valve" touch, or is it "grab the wires and wiggle" touch? It sounds more like a poor connection on the wiring, especially if you physically move anything—even a little. remove & reinsert the wires, or loosen & tighten the terminal screws a few times. If it's a loose\oxidized connection on the valve, that should make it go away, at least for some time.-1
-
-
It is in fact more lay finger on it material. I unplugged all the leads on the th, tp, th/tp side when testing the ohms. I didn't even realize there is a ground. What would be a good way to clean that up?
Thanks0 -
The first place I would look is for the grounding of the whole thing -- which includes the gas valve -- to the switchboard in your house. There should be, somewhere, a solid neutral wire going to the switchboard (it should be a white wire) and there should also be a solid ground (which should be green). If there is no 110 volts it still needs a ground -- the green wire -- but not the white. It may not have one.Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England-1 -
-
Also make sure that knob is actually in it's detent, it may just be on the edge.
BobSmith G8-3 with EZ Gas @ 90,000 BTU, Single pipe steam
Vaporstat with a 12oz cut-out and 4oz cut-in
3PSI gauge0
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 916 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements