24v ac for Honeywell vaporstat L408J1009?
Motorapido
Member Posts: 314
The product literature for the Honeywell vaporstat L408J1009 mentions 120v ac, but does not mention 24v ac. My pressuretrol currently operates at 24v ac, and I would like to add a vaporstat as my primary control with the pressuretrol still in place as my backup safety. I'd like to just add the vaporstat in series with the pressuretrol, but need to make sure that the L408J1009 can operate properly at 24v ac. Anybody have direct experience with this? I used Honeywell's customer service inquiry email to inquire, but you never know when a customer service rep reads a question if they will just look at the product spec sheet, see no mention of 24v ac and assume that 24v ac cannot work. If I could get directly to a product engineer there, I would be sure of the accuracy of the answer. Anyway, has anybody used a L408J1009 on 24v ac?
Yes. It’s just a switch. Only limit is maximum voltage and current rating. The device does not use power. Should work on milllivolt too.0
Just wire it in series with your Pressuretrol.0
- 120 Geothermal