Comparing Actual Electric Boiler Operation Costs to Gas
D107
Member Posts: 1,950
in Gas Heating
Given electricity costs, at least in the NE, electric boilers don't yet seem viable but I so loved the idea of removing indoor combustion from the process that I've looked into it. A 15KW electric boiler (equal to a 51,000 input gas boiler) would appear to use 15kw per hour if not modulated. I gather they are considered 98% efficient--the 2% going to piping and jacket losses. Does that 15kw rating include the electric for the circulators, LWCO, etc? I'm guessing it doesn't, since gas boilers also use circs, etc. which is an additional electric charge to gas costs. We used 775 therms for heat last year, which @$1.50 per therm total, adds up to about $1160. 775 therms is about 77,500mbh divided by 3.4mbh per kwh = 22,794kwh x $.25per kwh = $5700. Plus maybe circ, lwco usage. Sound right? Guess I'll have to wait for those new Emerson-Oak Ridge Labs Air Source Heat Pumps, which could still be quite a few years.
It doesn't look like you accounted for the inefficiency of the gas boiler.
Are you really paying $.25 per KWH?
Check out this spreadsheet.
Albert Einstein2 -
as @Zman correctly pointed out you didn't take the gas boiler efficiency into consideration.
775 therms burned at 80% ?? efficiency on gas= net btus of 620 therms at a cost of $1160 for gas. (You have to buy and pay for 775 therms to get 620 therms of heat)
620 therms (the heat you actually need) x 100000=62,000,000btu/3.41 btu/watt=18,181,818watts/1000=18,181kwh x $.25=
$4,525.25-1 -
Wow, thanks, great info, take me awhile to digest it. Re: electric charges, I counted supply, delivery, all other taxes and fees. Last month's bill was 441KWH for almost $114; that's almost $.26/kwh. Your table shows less than half that charge--a few years ago, yes--but obviously the area of the country you're in makes a big difference. As far as boiler efficiency, ours is an old WM about 75% AFUE. So to compare correctly do I just subtract 25% from the electric cost? Still not worth it.0
OK just saw Ed's explanation, thanks, so yeah even with boiler efficiency factored in, electric still costs 4x as much, at least in our area. So in what area of the country is electric $.06 kwh....
And here's another example I found online:
Simple example, if a gallon of oil costs $3 and has 140,000 btu's, that means you bought 46,666 btu's for a dollar (140,000/3). Now assume 82% efficiency, you get to keep 38,266 btu's in your house (46,666 *.82).
A kilowatt hour of electricity (kwh) has 3,412 btu's. If a kwh costs $.25 , that means you can by 4 of them for a dollar = 13,652 btu's ( 4 * 3,412). To make things simple, lets assume 100% efficiency for the electric boiler.
Based on this example, oil got us almost 3 times as much heat as electricity. You can go through a similar exercise for gas.0 -
Hydro-Quebec has a tiered system that offers low rates. They estimate 50% of the residential customers heat with electricity. probably why there are numerous electric boilers manufactured in the area, Thermo 2000, Thermolec are a few brands we see in the states.
Some homes I have been in have duel fuel boilers that use electricity to the limit, then automatically switch to gas.
Industrial customers may be in the 3 cents range up there.
Living the hydronic dream-1 -
The obvious point is that the relative cost of electric vs. gas vs. oil is going to depend on your rates for each one -- and various areas are wildly different. As @hot rod notes, in Quebec electricity -- even full retail -- is insanely cheap (I won't get into the politics of that, which are messy) while in New England, just over the border, the rates are insanely high. You have to do the math for your specific provider!Br. Jamie, osb
Hot rod
Yes the electric rates are cheap here. But for commercial applications, natural gas is a cheaper way to heat or use in a process system. Hydro Quebec has been mandated by the province to slowly bring the residential rates up. We do NOT do bi-energy with gas boilers. There are many residential oil/electric combination be it hot air or hot water. The consumer gets a better electric rate during non-peak hours or when above -12C. Below -12C, the electricity is billed at a higher rate. It becomes more economical to use oil. It is called the "DT" rates from Hydro Quebec.1 -
- 87.8K THE MAIN WALL
- 130 Chimneys & Flues
- 79 Pipe Deterioration
- 396 Solar
