Expansion Tank: does 2 = 1 + 1?
LesliePercy
Member Posts: 3
It seems that my system needs a rather large (50 litres) expansion tank, for which I don't really have room. Is it possible to use, instead, two 25 litre tanks? In parallel? In series?
In parallel, but connected at the same point to the system.Bob Boan
Yes with the above requirements, and installed so the circulator is pumping away from them, and on the supply side of the boiler.0
What Ironman, Jamie and Gordy said. We've done it.All Steamed Up, Inc.
Consulting0 -
I would have to rephrase the supply side of the boiler. Since some modcons like to be pumped into the boiler, or return side of boiler.0