Expansion Tank: does 2 = 1 + 1?
LesliePercy
Member Posts: 3
It seems that my system needs a rather large (50 litres) expansion tank, for which I don't really have room. Is it possible to use, instead, two 25 litre tanks? In parallel? In series?
0
Comments
-
In parallel, but connected at the same point to the system.Bob Boan
You can choose to do what you want, but you cannot choose the consequences.0 -
-
Yes with the above requirements, and installed so the circulator is pumping away from them, and on the supply side of the boiler.0
-
What Ironman, Jamie and Gordy said. We've done it.All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting0 -
I would have to rephrase the supply side of the boiler. Since some modcons like to be pumped into the boiler, or return side of boiler.0