underground Galvy
kcopp
Member Posts: 4,663
in Gas Heating
Looking at NFPA 54 they still allow gas piping underground using galvanized steel piping. Would that be any different w/ LP gas?
I would use the ConStab set up but the tees outrageously expensive.
This is an older version of NPGA 4001, it does allow galvanized pipe. Possibly some local codes might have an addendum preventing it. Local LP providers would have the best answer.
Living the hydronic dream-1 -
Thank you much HR.
This town in Maine has little in terms of regulation.0 -
Small OD soft copper, (Type L or K) will carry a lot of LP at the higher pressure of 10 PSI or so to the 2nd ounces regulator on the structure. Sleeve both ends above ground to protect from weed eater etc.
I have seen a few 50-60 year old LP installs. Always too small of a copper, one reg at tank....equipment was not fussy then...nor were the customers....relight pilots...no big deal. But the one case with galv fittings the furnace gas valve inlet screen was nearly plugged with flakes of some sort. Never saw this with all copper. FWIW
2 -
Old galvanized was a real problem with small pieces flaking off and plugging up pilots. We never allowed it on our lines or in house piping. We also did not like copper tubing for gas pilot lines preferred the aluminum tubing.0
What makes the aluminum better than the copper?0
I believe its because of the flaking issue again. Also I think it is less prone to corrosion if the sulfur content of the gas is higher....0
I just wish the tees were more reasonable in cost.... $$$!!0
- 123 Chimneys & Flues
