Thermostat help.
Have a new honeywell TH8320WF1029 with a steam boiler. The temperature is set to 68, and the reading on the thermostat which is connected to a remote sensor never shows more or less than 68. The boiler seems to go on for 10 minutes the off for around 10 then on again cycling very often.
1. Is this normal?
2. Is it bad for the boiler and should I switch thermostats?
3. Does this waste gas?
Thanks
This is on and off times I recorded
7:30 off
7:38 on
7:41 off
7:55 on
7:58 off
8:09 on
8:13 off
8:20 on
8:24 off0 -
Thermostats come from the factory set for five cycles per hour (5CPH), for forced air systems. Did you change that setting to one (1) Cycle per hour, the setting for steam?
Under Code "170" Select option "5"
Under Code 250, Select Option "1" - Cycles per hour0 -
1. It's normal -- if the thermostat is not set up properly.
2. It's not that bad for the boiler. It's not that good, either. There is no need to switch thermostats, though -- set it up properly for steam (1 cycle per hour) as @Fred said, and you should be fine.
3. Does it waste gas set up that way? Yes.Br. Jamie, osb
As others have said, you need to change it to run 1 or at the most, 2 cycles per hour "CPH" for your first stage heat.
Will check what it's set too and get back0
170 was set to 3 I changed it to 5 and there was only 240 I changed that to 1. Will report back0
Just double checking, these are the options for system type. I think we have a regular steam boiler. Which is the appropriate option? Unfortunately The installer did not go through options.
1 1 heat/1 cool conventional
2 1 heat/1 cool heat pump (no aux. heat)
3 Heat only (2-wire systems)
4 Heat only with fan
5 Hot water Series 20 system (power to open & close zone
valves/normally open zone valves) 6 Cool only
7 2 heat/1 cool heat pump (with aux. heat) 8 2 heat/2 cool multistage conventional
9 2 heat/1 cool multistage conventional 10 1 heat/2 cool multistage conventional 11 2 heat/2 cool heat pump (no aux. heat) 12 3 heat/2 cool heat pump (with aux. heat0 -
Don't know.albert0000 said:Just double checking, these are the options for system type. I think we have a regular steam boiler. Which is the appropriate option? Unfortunately The installer did not go through options.
How many stages of cooling and heating do you have?
If you only have steam heat and no cooling then #3 is correct for you.Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.
Sorry @albert0000 , when I looked up that thermostat, it was discontinued in March of 2016 and the codes I quoted you above were for its replacement #TH8321WF1001. You are correct, the setting for code #170 is "3"0
Great. Will set it and see what happens.
Thanks0 -
After you change the CPH setting give it a few hours to settle down.albert0000 said:Great. Will set it and see what happens.
ThanksSingle pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.
Ok, so I corrected the settings and the system doesn't cycle as much now. Thanks everyone for the help.
I have another thermostat TH8321WF1001 which is connected to a taco multi speed circulator that's connected to the boiler. This is for the basment radiators. Trying to make sure this one is setup correct because the motor seems to be running a lot. Went though system options and not sure about these.
1. Is this radiant heat or heat pump?
2. Cool stages, I'm assuming should be 0?
3. Radiant stages? 1,2, or 3
4. Backup heat type? Is this none even though the rest of the house has steam boiler?
5. Radiant cycles per hour? What's this?
Last one...
6. Indoor sensor type. 10k or 20k
Thanks tons0 -
Lessee, not heat pump, no cool, 1 heat, no backup, cycles/hour on the 1-3 range I think is the common recommendation, indoor sensor is used if you have a remote sensor wired to the stat.0
Thank you! Yes I have an indoor sensor. Not sure what the difference between 10k and 20k? Thanks0
The resistance of the sensor is dependant on its temperature. Different types have different values, Honeywell uses two, one that has a resistance of 10,000 ohms at 77*, the other 20,000. The paperwork of the sensor should tell you which one you have, probably 10k. If the displayed temperature is way off, try the other setting. You can also tell the stat to average the on-board & remote sensors.0