Repiping a steam boiler
Dave0176
Dave0176 Member Posts: 1,178
Unfortunately for the owner the plumber he hired placed a boiler double the size of the needed EDR. EDR measured at 188 he installed a Weil-McLain EG-40 at 325 sq ft. He had major wet steam and spitting air vents. The plumber never even pipped to at least Weil-McLains minimum specs, like a good plumber he pipped with a single 2" copper riser about 12" out of the boiler into the low hanging existing header. And ran a smallish 1-1/4 equalizer.
So I'm installing a 4" header two 3" boiler risers, and a Gifford loop as the wet returns go above the water line before the drop. A Honeywell two stage gas valve and vaporstat to control the oversized boiler.
DL Mechanical LLC Heating, Cooling and Plumbing 732-266-5386
NJ Master HVACR Lic# 4630
Specializing in Steam Heating, Serving the residents of New Jersey
https://heatinghelp.com/find-a-contractor/detail/dl-mechanical-llc
https://m.facebook.com/DL-Mechanical-LLC-315309995326627/?ref=content_filter
I cannot force people to spend money, I can only suggest how to spend it wisely.......
Paul S_3New England SteamWorksSWEIjonny88b_bzSteve Minnich
«1
  • EzzyT
    EzzyT Member Posts: 1,368
    @Dave0176 what a beauty of a repipe, that steam is going to super dry.
    E-Travis Mechanical LLC
    Etravismechanical@gmail.com
    201-887-8856
  • Dave0176
    I'm hoping so @EzzyT that's why the 4" header. Also of course the plumber never installed a skim tapping so it's never been skimmed. So I'm gonna run the crap out of it then skim it, then when heating season starts I'll come back skim more then wash it out. He also needs to address main venting as there isn't enough.
    wyo
  • EzzyT
    Its a shame that boiler is way over sized but the 2 stage firing set up will handle that. How that washing/wand rig you have working out for you?
    201-887-8856
  • Fred
    Fred Member Posts: 8,542
    A piece of ART!!
  • EzzyT
    @Fred it truly is a piece of art
    201-887-8856
  • Dave0176
    It the greatest invention @gerry gill ever came up with. I'm obsessed with it, and its results.
  • ChrisJ
    ChrisJ Member Posts: 16,863
    edited September 2016
    I don't think that smoke pipe is to code in the pictures. :)
    Ah, the signature Dave S bend equalizer. Dead giveaway for your work.
    Looks clean as always.
    I'm curious, how does it perform on low fire? How bad was the excess o2?
  • Paul S_3
    Paul S_3 Member Posts: 1,288
    beautiful install @Dave0176 .....its great to see us all install these beautys ......its like everyone else just hacks them in
    ASM Mechanical Company
    Located in Staten Island NY
    347-692-4777
    ASMMECHANICALCORP@GMAIL.COM
    ASMHVACNYC.COM
    https://heatinghelp.com/find-a-contractor/detail/asm-mechanical-company
  • EzzyT
    Agreed @Paul S
    201-887-8856
  • That I'll work @Dave0176 ! Bravo! Taking the time to remove the original header and straighten out the supplies for your header: Priceless! Your customer should be well pleased with such workmanship.
    newenglandsteamworks.com
    SWEI
  • KC_Jones
    KC_Jones Member Posts: 5,885
    If I am seeing it correctly it looks like the plumber put some steel across the top of the pad to allow for the boiler to sit there. I guess the fact that it didn't fit the pad wasn't even enough of a clue it was too big. I feel so bad for people spending all that money....twice just to get a quality job. The existence of crap work in any field truly upsets me. Think of all the waste we have in this country as a result?!
    Dave keep up the good work your pride is obvious, fantastic work as usual. Consider an apprentice some day when you get older and need to pass along your skills to someone. We need to perpetuate your work ethic along with many others on this wall!
    I too am curious about your low fire set up and how it performs.
    2014 Weil Mclain EG-40
  • Dave0176
    When I fire it and do the combustion test I'll post the results of both high and low fire. The Testo 320 is ready!!
    KC_JonesChrisJ
  • Dave0176
    This boiler was originally installed on Dec 23, 2010 as an emergency. Wasn't to bad to remove all the plugs because I had told the owner to hit it with PB Blaster at least every couple days. Had to to put the 48" ridgid to work on those plugs but we got them out.
  • EzzyT
    I hear yeah I had to do the same on the steamer I just repiped
    201-887-8856
  • New England SteamWorks
    New England SteamWorks Member Posts: 1,528
    <3
  • EzzyT
    Haha, there is no competition were both here to do our part to rid the industry of the hacks
    201-887-8856
    ChrisJPaul S_3
    Steamhead Member Posts: 17,899
    Beautiful. Just beautiful.
    Consulting
  • JUGHNE
    JUGHNE Member Posts: 11,469
    Great improvement!
    Did the original installer put the vaporstat & 0-5 PSI gauge on the boiler along with the 2" CU pipe? Seems overkill for a blotched job by him.
    I have visions of a lot of short cycles with the way it was, being oversized and cutting out on less than a pound.
  • Dave0176
    Job is complete, ran it, was dirty as hell, skimmed it, still dirty, so I got my trusty wand out and washed it good. Everything ran quietly, no more spitting air vents, no banging, fire cycles off hi fire at 10oz, and kicks back on at 4. The POS stock pressuretrol even works lol. It kicks the fire completely at 1.5 psi.
    Had to adjust the gas valve to get proper gas pressures, took a combustion test and this is for @ChrisJ the high fire excess air was 137% low fire it was 258%.
    The number were hi fire
    265 degree stack, 11.5% oxygen, CO 8 ppm, CO2 6%
    Low fire
    248 stack, 15.6 O2, CO 2ppm, CO2 3
    b_bzjonny88Paul S_3Steve Minnich
  • ChrisJ
    @Dave0176 Those numbers, that has to be after the drafthood, no?
    What was the calculated efficiency?
  • jonny88
    jonny88 Member Posts: 1,139
    I hope your customer sees this thread.Beautiful install.We can all learn from this.Even the little doggy seems happy.
  • Dave0176
    Yep that was measured at 12" up in the stack, efficiency was 84.3.
  • JUGHNE
    I thought you checked the combustion gases before the draft hood? 12" up the stack would have the dilution air from the basement included via the draft hood?
    Not to argue, just thought that was I read. I have done checks by sticking probe thru the hood to get the actual gases off the heat exchanger, it always seems awkward and more of a hot place than I want to be.
    Paul S_3Hatterasguy
  • Dave0176
    Yeah the instructions list to test 12" up the stack, I could check before the draft hood.
  • Dave0176
    JUGHNE said:
    Great improvement!
    No I the homeowner added those items himself.
  • Paul S_3
    that explains the low stack temp and hi O2.....
    347-692-4777
    ASMHVACNYC.COM
  • JUGHNE
    So if I have a power burner without a drafthood, I would check gases and temp right off the fire without the added benefit of room air cooling the exhaust and adding O2 from that air.
    So one would come up with quite different numbers in each case. I believe the temp tester knows the room temp and takes that into account when calculating efficiency based on exhaust temp inside the draft hood before dilatation air is added.
    Again I am just here to learn....it never ends.
  • warno
    warno Member Posts: 229
    Damn, You guys do magic with threaded pipe. Good job. Being a welder I personally hate threaded connections but it does make things come apart easier.
  • ChrisJ
    Swing joints are a must on a boiler like this, no?
    Some welders do magic too.
  • Hap_Hazzard
    Hap_Hazzard Member Posts: 2,917
    Plasma cutters make things come apart a lot easier! :smiley:
    Paul S_3SWEICLamb
  • ChrisJ
    So does a Sawzall. :)
  • Dave0176
    Lets not forget an angle grinder. One of my favorite tools.
  • EzzyT
    Band saw does a better job with no vibrations
    201-887-8856
    SWEI
  • Hap_Hazzard
    Have you ever used a plasma cutter? You'll never take a sawzall seriously after you use a plasma cutter.
  • ChrisJ
    I was finally able to get my own angle grinder this week, a plasma cutter is likely never happening in my life time.
    I had my dad's grinder, he wanted it back after several years. :)
  • EzzyT
    Plasma cutter are great but not practical in someone home
    201-887-8856
  • warno
    Here's some of my more recent work on my own junk. Ok, thread jacking done, sorry.
    Again, beautiful piping.
    Hap_HazzardChrisJCanuckerSWEI
  • Hap_Hazzard
    Nice fillet! Is that stainless?
  • Sailah
    Sailah Member Posts: 826
    Walking the cup!
    I live TIG welding but I'm still an amateur
    Peter Owens
    SteamIQ
  • warno
    Yep, it's stainless. 3" sch40 pipe with a 1" sch40 connection.