What a disaster
Dave0176
Dave0176 Member Posts: 1,178
Got a call to service and find out why so little heat. I found this disaster, and no the owner won't replace it. Anyway I had to bleed the loops and found a the extrol tank pissing, so I replaced that, (it isn't even piped properly, in fact the whole boiler isn't piped properly, wrong minimum pipe sizes, pumped to the return). I also thought it was under firing which I was right, I clocked the gas meter and found it burning 425,000 BTU, checked pressure was good, so I replaced the gas valve too, and now we're burning the proper 550,000 BTU. Anyway you can lead a horse to water but..........
DL Mechanical LLC Heating, Cooling and Plumbing 732-266-5386
NJ Master HVACR Lic# 4630
Specializing in Steam Heating, Serving the residents of New Jersey
https://heatinghelp.com/find-a-contractor/detail/dl-mechanical-llc
https://m.facebook.com/DL-Mechanical-LLC-315309995326627/?ref=content_filter
I cannot force people to spend money, I can only suggest how to spend it wisely.......
Steve Minnich
  • SWEI
    SWEI Member Posts: 7,348
    Yikes!
    Were you able to eliminate the rollouts that left all those char marks?
    kcopp
  • njtommy
    njtommy Member Posts: 1,105
    Unbelievable. I think you just adopted a problem child.
  • Steve Minnich
    Steve Minnich Member Posts: 2,868
    Ya gotta love the switches mounted directly to the pumps.
    Steve Minnich
  • Abracadabra
    Don't have to label the switches then :D
    Steve Minnich
  • Ironman
    Ironman Member Posts: 7,771
    Why the shutoff valve AFTER the gas valve? Was some knucklehead trying to throttle the gas down because of the flame roll out on the left side?
    Bob Boan
    GordyRich_49
  • kcopp
    kcopp Member Posts: 4,600
    From the looks of the roll out I wonder if the chimney is pulling a draft...prob not lined.
  • Gordy
    Gordy Member Posts: 9,546
    Be the only reason I can think of. Genius waiting to happen......................and still waiting.
  • Dave0176
    I did a combustion test with my testo and everything seemed alright, had good draft. Who knows what shoemaker worked on this thing in the past.
    ChrisJ
  • EzzyT
    EzzyT Member Posts: 1,377
    Dave you'll be back there plenty nurturing that disaster.
    E-Travis Mechanical LLC
    Etravismechanical@gmail.com
    201-887-8856