too many cycles
al54
Member Posts: 4
in Gas Heating
I have a alpine 150 boiler installed sept 27 2013 . i have 5 heat zones and a hot water storage. 1850 sq ft stucco frame house no wall insulation . to date the boiler has cycled more than 65000 times, I cant imagine this is correct but I cannot get US Boiler to discuss my situation . can you provide me some info
thanks,
al54
thanks,
al54
That an average of one cycle every 19 minutes, which means during heating season you are probably cycling even more frequently.
Many zones with small heat loads will do this to low mass boilers. There are things you can do to reduce cycling like combining zones together, or installing a buffer tank.Hydronics inspired homeowner with self-designed high efficiency low temperature baseboard system and professionally installed mod-con boiler with indirect DHW. My system design thread: http://forum.heatinghelp.com/discussion/154385
System Photo: https://us.v-cdn.net/5021738/uploads/FileUpload/79/451e1f19a1e5b345e0951fbe1ff6ca.jpg0 -
other than your recommendations can the settings be adjusted on the sage 1 system and or the thermostats also be timed better0
by the way Brewbeer I forgot to thank you for your comment so thanks
al540 -
al54 what is your location? If you e-mail me I can connect you with someone who will help you from Burnham. My e-mail is gastc@cox.net0
Burnham would like you to have your installer/contractor/service person call them directly from your facility and they will walk them through a solution to your problem.0
5 zones in an 1850 sqft house?
In my house I was getting excessive cycling due to Mum in law having apt attached to house.She has roughly 800sqft.I combined her zone with our downstairs heating zone.I went from 45 cycles to 2 per day.Boiler is firing at lowest oiutput.Will be interesting to compare gas bills over the year but the cycling issue has stopped which I am happy about.On average including hot water I am cycling 4-6 times a day.Boiler goes to 115k and house is 2750sqft build like an average Long Island house....0 -
Hi Tim , im in westchester cty, ny. my email is0
Boiler more then likely over sized and as others have said zoning could have a lot to do with it. Best approach is a new room x room/ zone x zone heat loss, emitter measurements and calculation of btu/hr capability of them. From there a curve and modulation rate adjustment probably and you may want to look into this providing you have the correct version of the Sage Control
https://file.ac/5CdWisGaB8A/Sage Zone Control Value Sheet.pdfThere was an error rendering this rich post.
- 85.7K THE MAIN WALL
- 49 Biomass
- 71 Chimneys & Flues
- 92 Geothermal
- 149 Indoor-Air Quality
- 3.2K Oil Heating
- 59 Pipe Deterioration
- 847 Plumbing
- 5.8K Radiant Heating
- 371 Solar
- 14.5K Strictly Steam
- 50 Water Quality
- 38 Industry Classes
- 15 Recall Announcements
