connecting 2 thermal oil boilers

Options
mshkry
mshkry Member Posts: 3
i Have a 500,000 BTU oil boiler and buying another 300,000 BTU . How to connect both of them to give higher rating as well to act as standby for each others ? Will the same piping work ?

Comments

  • vaporvac
    vaporvac Member Posts: 1,520
    Options
    Is this for steam?
    Two-pipe Trane vaporvacuum system; 1466 edr
    Twinned, staged Slantfin TR50s piped into 4" header with Riello G400 burners; 240K lead, 200K lag Btus. Controlled by Taco Relay and Honeywell RTH6580WF
  • mshkry
    mshkry Member Posts: 3
    Options
    Oil ..
  • Steamhead
    Steamhead Member Posts: 16,835
    Options
    How does the heat get from the boiler to the rooms? By hot water, or steam?
    All Steamed Up, Inc.
    Towson, MD, USA
    Steam, Vapor & Hot-Water Heating Specialists
    Oil & Gas Burner Service
    Consulting
  • Paul48
    Paul48 Member Posts: 4,469
    Options
    Pipes..
    ZmanvaporvacBrewbeer
  • mshkry
    mshkry Member Posts: 3
    Options
    It's industrial boiler . Oil goes in pipes to heat water and other chemicals .
  • jumper
    jumper Member Posts: 2,248
    Options
    First inclination is not to mix circuits. Separate heat exchangers. If you scorch thermal fluid the entire circuit including boiler and heat exchanger has to be purged and cleaned.
  • SWEI
    SWEI Member Posts: 7,356
    Options
    I'm thinking primary/secondary, but really need to know more about the existing piping setup. Got a diagram? Photos?