connecting 2 thermal oil boilers
mshkry
Member Posts: 3
in Oil Heating
i Have a 500,000 BTU oil boiler and buying another 300,000 BTU . How to connect both of them to give higher rating as well to act as standby for each others ? Will the same piping work ?
Is this for steam?Two-pipe Trane vaporvacuum system; 1466 edr
Twinned, staged Slantfin TR50s piped into 4" header with Riello G400 burners; 240K lead, 200K lag Btus. Controlled by Taco Relay and Honeywell RTH6580WF0 -
Oil ..0
How does the heat get from the boiler to the rooms? By hot water, or steam?
Consulting0 -
It's industrial boiler . Oil goes in pipes to heat water and other chemicals .0
First inclination is not to mix circuits. Separate heat exchangers. If you scorch thermal fluid the entire circuit including boiler and heat exchanger has to be purged and cleaned.0
I'm thinking primary/secondary, but really need to know more about the existing piping setup. Got a diagram? Photos?0