Downsizing Munchkin 399M by Replacing Burner
16sail
16sail Member Posts: 3
The prior homeowners installed a grossly oversized modcon (Munchkin 399M) in our 3,500 sqft New England home.
Our heating contractor suggested replacing the burner with one from a Munchkin 199M to improve efficiency. He indicating this is a very simple exercise, though I suspect the part is not cheap.
Is this a sensible path to follow? Any downsides? Are there any other actions we can take besides a rip and replace of the boiler?
  • kcopp
    kcopp Member Posts: 4,675
    edited November 2015
    The only real answer to that question is a call to HTP.
    Grossly oversized is an understatement.
    HTP, Inc.
    272 Duchaine Boulevard
    New Bedford, MA 02745
    Telephone: 800 323 9651
    Telephone: 508 763 8071
    Fax:508 763 3769
    E-mail: sales@htproducts.com
  • Ironman
    Ironman Member Posts: 7,903
    I doubt if you can do it, but if the factory says it okay, get it in writing with detailed instructions. Also, make them give you a new rating tag for the boiler. Otherwise, the person doing it is totally liable for altering the appliance and any results, which could included personal injury or death.
    Another solution which would be less expensive than a new boiler would be to install a properly sized buffer tank.
    Bob Boan
    Zman
  • Rich_49
    Rich_49 Member Posts: 2,783
    Your contractor probably should have mentioned or suggested a heat loss be performed . @ 30BTUh sq ft your home is only 105,000 . The 199 is also grossly oversized my friend . Maybe you should find another contractor that is willing to do the right thing . This would be a much better fit and a new warranty also . You won't believe the price point either .
    http://www.htproducts.com/UFT-Boiler.html
    Sticking a smaller combustion assembly into a wrong sized Giannoni Heat exchanger in a machine with a serial number that is more than likely damn near out of warranty is just plainly a terrible idea . I highly doubt HTP will allow this either . Contact Emerson Swan in Randolph and ask them who might be the best for you to contact in your area to look at this job . They will know who to put you in touch with to get this done right .
    732-751-1560
    Rich McGrath 732-581-3833