Welcome! Here are the website rules, as well as some tips for using this forum.
Need to contact us? Visit https://heatinghelp.com/contact-us/.
Click here to Find a Contractor in your area.
If our community has helped you, please consider making a contribution to support this website. Thanks!
Placement of Water to air heat exchanger
Options
rico7467
Member Posts: 40
Is it more efficient to place my heat exchanger before the a-coil and blower oron the intake side of my horizontal airhandler or on the outtake side of the air handler after the blower
0
Comments
-
It should be placed on the supply side. Most blower motors cannot take the heat produced from the hot water coil. They are designed to have 70* return air to cool the motor, not 140*+ air that will come off of the hot water coil.Bob Boan
You can choose to do what you want, but you cannot choose the consequences.2
Categories
- All Categories
- 87.3K THE MAIN WALL
- 3.2K A-C, Heat Pumps & Refrigeration
- 61 Biomass
- 429 Carbon Monoxide Awareness
- 120 Chimneys & Flues
- 2.1K Domestic Hot Water
- 5.8K Gas Heating
- 115 Geothermal
- 166 Indoor-Air Quality
- 3.7K Oil Heating
- 77 Pipe Deterioration
- 1K Plumbing
- 6.5K Radiant Heating
- 395 Solar
- 15.7K Strictly Steam
- 3.4K Thermostats and Controls
- 56 Water Quality
- 51 Industry Classes
- 50 Job Opportunities
- 18 Recall Announcements

