Boiler problem
rock1972
Member Posts: 7
I have to hit the reset button on my boiler every couple of days. Usally at nite when i gets colder. It will run fine then. I had it cleaned and the thermostat replaced in the past week . All help is wanted. Thanks
I can't load a pic but it is a hot water boiler and it has only 1 rest button.0
Is this oil or gas? Is the reset on the burner control system?0
oil the reset is up on the side of the boiler it has the aqua stat in the same box0
Do you know if this shuts down on high limit...water/boiler overheating? Maybe lack of water flow. I'm don't see any oil in my area. There are many more here who know about your situation and will probably jump in. Is there any labeling on the reset switch that pops? Being located with the aquastat implies water temp issue IMHO. Pictures get a lot of eyes on the problem.1
After i hit the reset it has been running fine I just do not know what can cause the reset to be tripped and i have never seen just on reset on a boiler it is an americanstandard a34m with an carlin burner.
I do not think it is over heating because it will call for heat on the second floor or for hot water and run fine .
How long has it been since it was serviced? Nozzle, filter, etc need to be changed at least yearly. Sometimes more often depending upon how much fuel is burned.
The reset button means there's been an ignition failure. You need to call an oil burner tech.Bob Boan
You can choose to do what you want, but you cannot choose the consequences.1 -
I just had it serviced. I have had a tech out here twice this week. Iwill call him in the morning thanks.
i watched the tech he changed the nozzle,oil filter and the filter on the burner,and cleaned the boiler. also changed the thermostat.
If it is burner lockout; then the spark ignitor to establish flame or the eye/sensor to prove flame could be at fault; assuming oil is flowing. Does this system have one retry on flame out before lockout requiring reset?0
This should be posted in the Oil heating section. It could be a dozen reasons why it is locking out. Pics and more boiler/burner info is needed. Was it locking out before the service?0
- 120 Geothermal