Low water cut off turned boiler off but auto feed did not happen
rrwitherspoon
Member Posts: 104
Glass 1/3 full but still above lowest mark on boiler. The thermostat calling for heat...red light on LWCO blinking turned boiler off. Dot after numbers on programmable water feed comes on but no automatic feed water given. Boiler comes on again and cycle repeats itself. Shouldn't the programmable water feed stop this cycling and satisfy good water level
What kind of water feeder? Some feeders have a strainer that needs to be cleaned periodically.0
programmable water feeder hydrolevel company VXT-24
I had to manually push feeder button myself to give water to stop boiler cycling off
Turned off boiler twice before I decided to feed myself fter boiler cooldown as not to crack boiler0 -
Not very familiar with the VXTs, since I use MM LWCO and feeders, but what is the feed delay set for? From the manual
A small indicating light in the lower right hand corner of the digital feed counter illuminates whenever the low
Maybe it's in lockout or delay?
water cut-off is calling for a feed. The light remains on for the duration of the call from the cut-off regardless of
the mode the feeder is in (delay, feed or lock-out). The light turns off when the cut-off is satisfied and stops
calling for a feed.0 -
ok I will ask tech to check that
Does the LWCO sensor need cleaning with yearly maintenance?
It is a Mcdonnell White unit.0 -
opps McDonnell miller0
Says right on front of unit that it should be inspected and cleaned annually but tech said it did not require this because
it has a stirrer in it that keeps crude off??? Why would he say that if it says otherwise?0 -
He said he would only inspect it if there was an issue but it seems he should he inspect annually so there will be no issue
I do not want to lose this expensive boiler0 -
I think another question is, "Why does it turn off on low water?" Perhaps you have slow wet returns due to sludge build-up. If so do you have a way to clean them out? Has the boiler been WELL skimmed? While you obviously want the water-feed to work properly, the introduction of excess fresh water is the surest way to lose that expensive boiler.Two-pipe Trane vaporvacuum system; 1466 edr
Did you have to feed water to get the system to turn back on? It doesn't sound like it from your original prompt. If that is the case, it sounds to me as though the LWCO and feeder may be working correctly. There is sometimes a delay on the feed set on those feeders, to prevent feeding and consequent flooding of the boiler in the event the problem is slow returns or water backing out of the boiler under pressure. Check that all first before assuming that the feeder is the problem -- don"t shoot the messenger!Br. Jamie, osb
Yes, I think the sludge filled condensate was the issue. I made the system call for heat sitting and watching boiler control behavior and I was able to hear sludge condensate return to pipe and drop off into boiler or lower pipe. That was incredible to hear. It was pretty loud. The LWCO and auto feeder now behaving normally ie no flashing red light. The pressure issues
seem to e resolved also. Pressure stays below 1 psi.Should I do something about the sludge.0 -
Heh..rrwitherspoon said:Says right on front of unit that it should be inspected and cleaned annually but tech said it did not require this because
1 - stirrer = strainer?
2 - strainer needs periodic maintainance.
3 - what kind of a "tech" was this?
Yes, clean the sludge out.rrwitherspoon said:Should I do something about the sludge.
Oh some confusion. I want to be clear.The Mcdonnell- Miller LWCO says that the probe should be inspected annually and clean if needed. The tech from Plumbing and Heating Company during yearly maintanence says he only inspects probe if there is something wrong with it. Does not seem interested in preventative manitanence only replacement.0
how does one clean sludge out of one pipe steam system?
I have book The Lost Art does not describe how to remove sludge from piping.0 -
Sorry two conversations here LWCO maintenance and sludge in pipes.0
Open up sections as needed and wash out with a hose.rrwitherspoon said:how does one clean sludge out of one pipe steam system?
And they make more money on replacements because they are not doing proper maintenance which causes equipment failure sooner. Preventative maintenance is never a bad idea and any "mechanic" that thinks otherwise is not a mechanic. Oh that's right they are "Techs". No offense to anyone intended I just get tired of people either being taught to do bad work or just doing it on their own.rrwitherspoon said:Does not seem interested in preventative manitanence only replacement.
Yes I am getting that impression
I do not know what to do.
I am happy with standing pilot.They are trying to convince me to get electronic ignition but I think that just sets me up for more issues.
My heating bill is good since I switched from oil to gas unit. I do not think it uses a lot of energy.0
- 87K THE MAIN WALL
- 115 Chimneys & Flues
- 106 Geothermal
- 983 Plumbing
- 389 Solar