Honeywell Zone Valve V8043 wiring
BuddyB
Member Posts: 1
in Gas Heating
Hello ... I recently had a 6 zone heating system installed. My problem is, the 6th zone, although installed, was not wired. The installer was hospitalized during the installation and has not been able to return. The zone valve in question is a Honeywell V8043. It has a pair of red wires and a pair of yellows. There are two 40VA transformers installed (3 zones per). I can follow the existing wiring but the question I have is 'Does it matter which of the 2 red leads or 2 yellow leads are used without having to open the valve itself to see the wiring? I hope I'm making sense here. Thanks
No
As long as yellow go to yellow and the red goes to red.0 -
Your comment doesn't make sense. The yellow leads ARE the motor leads and the red ARE the end switch. I'm talking about the actuator, not any system wiring.Bob Boan
Wire as follows (corrected)
Wire the hot lead (R) from the transformer to one yellow lead, wire the other yellow lead to one thermostat lead, A series circuit and it does not matter which motor lead goes to which connection. The two red leads (end switch) go to "T T" on the relay. It does not matter which red goes to which "T".
Thanks Pughie just one too many sentences.0 -
Zone Valve Relay panels
How about investing in one of the several out there zone valve relay panels? With 6 zones it would make a much simpler neater job. You wouldn't even need to use the zone valve end switches if you chose not to.
Timmie, go over your last post would you?
John Pughe0 -
Zone Valve Panels:
I think that guy already has a 6 zone, zone valve panel. The installer got sick and couldn't finish the job. He needs to get the last zone wired so it works.
It can be confusing but look at how the other 5 zones are wired and what colors go to where.0 -
Panels
Ice,
I interpreted him saying "he had 2 transformers" as being separate transformers, but you could be right as there are 2 transformers in the 6 zone panels.
john0
