Welcome! Here are the website rules, as well as some tips for using this forum.
Need to contact us? Visit https://heatinghelp.com/contact-us/.
Click here to Find a Contractor in your area.
Electronic water feeder/lwco for WeilMcClain Model 80
Options
JEMM55
Member Posts: 47
Which feeder/lwco can i use to replace my McConell 47-2?
I want to be able to monitor feedwater s well.
I want to be able to monitor feedwater s well.
0
Comments
-
can i use a vxt?
850'000 btu with.powerflame burner0 -
can i use a vxt?
850'000 btu with.powerflame burner0 -
-
On 80 series boilers
there should be two tappings on the front for probe-type low-water cutoffs. We'll put a standard unit in the upper tapping and have that control the VXT. The lower tapping gets a manual-reset LWCO. This not only brings the LWCO setup up to CSD-1 standards, but it gets rid of the moving parts found in the 47-2.
Here's a pic of a 4-80 we installed that way. The VXT is around back.All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting0
This discussion has been closed.
Categories
- All Categories
- 85.6K THE MAIN WALL
- 3K A-C, Heat Pumps & Refrigeration
- 51 Biomass
- 423 Carbon Monoxide Awareness
- 71 Chimneys & Flues
- 1.9K Domestic Hot Water
- 5.2K Gas Heating
- 92 Geothermal
- 149 Indoor-Air Quality
- 3.2K Oil Heating
- 60 Pipe Deterioration
- 850 Plumbing
- 5.8K Radiant Heating
- 375 Solar
- 14.5K Strictly Steam
- 3.2K Thermostats and Controls
- 51 Water Quality
- 38 Industry Classes
- 55 Job Opportunities
- 18 Recall Announcements