Welcome! Here are the website rules, as well as some tips for using this forum.
Need to contact us? Visit https://heatinghelp.com/contact-us/.
Click here to Find a Contractor in your area.
Electronic water feeder/lwco for WeilMcClain Model 80

JEMM55
Member Posts: 47
Which feeder/lwco can i use to replace my McConell 47-2?
I want to be able to monitor feedwater s well.
I want to be able to monitor feedwater s well.
0
Comments
-
can i use a vxt?
850'000 btu with.powerflame burner0 -
can i use a vxt?
850'000 btu with.powerflame burner0 -
-
On 80 series boilers
there should be two tappings on the front for probe-type low-water cutoffs. We'll put a standard unit in the upper tapping and have that control the VXT. The lower tapping gets a manual-reset LWCO. This not only brings the LWCO setup up to CSD-1 standards, but it gets rid of the moving parts found in the 47-2.
Here's a pic of a 4-80 we installed that way. The VXT is around back.All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting0
This discussion has been closed.
Categories
- All Categories
- 84.3K THE MAIN WALL
- 2.9K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 417 Carbon Monoxide Awareness
- 44 Chimneys & Flues
- 1.8K Domestic Hot Water
- 4.8K Gas Heating
- 120 Geothermal
- 156 Indoor-Air Quality
- 3K Oil Heating
- 57 Pipe Deterioration
- 794 Plumbing
- 5.4K Radiant Heating
- 370 Solar
- 14.1K Strictly Steam
- 3.1K Thermostats and Controls
- 54 Water Quality
- 39 Industry Classes
- 80 Job Opportunities
- 22 Recall Announcements