Electronic water feeder/lwco for WeilMcClain Model 80
Options
JEMM55
Member Posts: 47
Which feeder/lwco can i use to replace my McConell 47-2?
I want to be able to monitor feedwater s well.
I want to be able to monitor feedwater s well.
0
Comments
-
can i use a vxt?
850'000 btu with.powerflame burner0 -
can i use a vxt?
850'000 btu with.powerflame burner0 -
-
On 80 series boilers
there should be two tappings on the front for probe-type low-water cutoffs. We'll put a standard unit in the upper tapping and have that control the VXT. The lower tapping gets a manual-reset LWCO. This not only brings the LWCO setup up to CSD-1 standards, but it gets rid of the moving parts found in the 47-2.
Here's a pic of a 4-80 we installed that way. The VXT is around back.All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting0