pressure test new system?
ChrisJ
ChrisJ Member Posts: 17,068
Once I'm finally done piping the new boiler in I'm wondering if I should pressure test it or not.
All pipes are really tight and I used Ward cast fittings.  Most fittings I used Megaloc dope alone.  Any questionable connections like into the old mains I used the Megaloc and blue monster tape.  I have king valves and a return valve so testing is possible.
I can setup to do a pressure test but its kind of a pain.  What should I do?  Take the time to setup and test it with air or just fillerup and light the fire?
  • testing for leaks
    can you just overfill the boiler up to the dry return, and leave it over night. thats how we did the test.--nbc
    Jamie Hall Member Posts: 26,834
    You could...
    pressure test the near boiler piping, if you really wanted to -- but I like nbc's idea.
    Do not pressure test the rest of the system -- neither traps nor vents play nicely with pressures much over 5 psi.
  • ChrisJ
    ok
    So I guess its safe to say the pros don't usually pressure test the block and near boiler piping?
    I just want to try and follow what the pros do.  I figure I should be safe that way for the most part.
  • Long Beach Ed
    Long Beach Ed Member Posts: 1,806
    The Block
    We pressure test each boiler before we install it.  We cap the fittings and pressurize it.
    Over the years we've installed hundreds of Burnham boilers - they are our favorates.  Never found a leaker.
    We don't pressurize anything else, unless there is a hot water loop on a steam boiler.  We'll pressurize that too.
    Wet returns?  If they are under the ground we assume they leak.