Error Code for Carrier Weather Maker 9200
MacPHJr
MacPHJr Member Posts: 66
Looking for an error code "45" for Carrier Weather Maker 9200 model #58MXB? No literature on site and cant get through to text support. Any ideas?
  • Eugene_Silberstein
    Eugene_Silberstein Member Posts: 349
    From Carrier's website
    ERROR CODE 45 - CONTROL CIRCUITRY LOCKOUT
    Auto-reset after one hour lockout due to;
    - Gas valve relay stuck open - Flame sense circuit failure
    - Software check error
    Reset power to clear lockout. Replace control if status code repeats.
  • MacPHJr
    Control Board and Inducer fan replaced in May by another company. Vent sized appropriately, condensate drains are clear. Unit has proper pitch.
    Heats up quickly then shutsdown on error code. Then starts back up.
    Any ideas?
  • Tim McElwain
    Tim McElwain Member Posts: 4,656
    Check the
    flame rod pull it and clean and re install check the microamp signal should be between 2 to 10 microamps.
  • MacPHJr
    Thanks
    Thanks Tim. Is the flame rod the same as the igniter? Are micro amps AC or DC?
  • MacPHJr
    My bad
    Just re-read your post Tim. You said check amps not voltage. Thanks.
  • Tim McElwain
    If the system
    has a hot surface igniter then it may also be used as a sensor or there may be a separate sensor. You are looking to measure DC microamps.