Error Code for Carrier Weather Maker 9200

Options
MacPHJr
MacPHJr Member Posts: 66
Looking for an error code "45" for Carrier Weather Maker 9200 model #58MXB? No literature on site and cant get through to text support. Any ideas?

Comments

  • Eugene_Silberstein
    Eugene_Silberstein Member Posts: 349
    Options
    From Carrier's website



    ERROR CODE 45 - CONTROL CIRCUITRY LOCKOUT

    Auto-reset after one hour lockout due to;

    - Gas valve relay stuck open - Flame sense circuit failure

    - Software check error

    Reset power to clear lockout. Replace control if status code repeats.
    Auto-reset after one hour lockout due to;

    - Gas valve relay stuck open - Flame sense circuit failure

    - Software check error

    Reset power to clear lockout. Replace control if status code repeats.

    There was an error rendering this rich post.

  • MacPHJr
    MacPHJr Member Posts: 66
    Options
    Error Code for Carrier Weather Maker 9200

    Control Board and Inducer fan replaced in May by another company. Vent sized appropriately, condensate drains are clear. Unit has proper pitch.



    Heats up quickly then shutsdown on error code. Then starts back up.



    Any ideas?
  • Tim McElwain
    Tim McElwain Member Posts: 4,625
    Options
    Check the

    flame rod pull it and clean and re install check the microamp signal should be between 2 to 10 microamps.
  • MacPHJr
    MacPHJr Member Posts: 66
    Options
    Thanks

    Thanks Tim. Is the flame rod the same as the igniter? Are micro amps AC or DC?
  • MacPHJr
    MacPHJr Member Posts: 66
    Options
    My bad

    Just re-read your post Tim. You said check amps not voltage. Thanks.
  • Tim McElwain
    Tim McElwain Member Posts: 4,625
    Options
    If the system

    has a hot surface igniter then it may also be used as a sensor or there may be a separate sensor. You are looking to measure DC microamps.