Error Code for Carrier Weather Maker 9200
MacPHJr
Member Posts: 66
in Gas Heating
Looking for an error code "45" for Carrier Weather Maker 9200 model #58MXB? No literature on site and cant get through to text support. Any ideas?
0
Comments
-
From Carrier's website
ERROR CODE 45 - CONTROL CIRCUITRY LOCKOUT
Auto-reset after one hour lockout due to;
- Gas valve relay stuck open - Flame sense circuit failure
- Software check error
Reset power to clear lockout. Replace control if status code repeats.Auto-reset after one hour lockout due to;
- Gas valve relay stuck open - Flame sense circuit failure
- Software check error
Reset power to clear lockout. Replace control if status code repeats.There was an error rendering this rich post.
0 -
Error Code for Carrier Weather Maker 9200
Control Board and Inducer fan replaced in May by another company. Vent sized appropriately, condensate drains are clear. Unit has proper pitch.
Heats up quickly then shutsdown on error code. Then starts back up.
Any ideas?0 -
Check the
flame rod pull it and clean and re install check the microamp signal should be between 2 to 10 microamps.0 -
Thanks
Thanks Tim. Is the flame rod the same as the igniter? Are micro amps AC or DC?0 -
My bad
Just re-read your post Tim. You said check amps not voltage. Thanks.0 -
If the system
has a hot surface igniter then it may also be used as a sensor or there may be a separate sensor. You are looking to measure DC microamps.0
This discussion has been closed.
Categories
- All Categories
- 86.5K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 423 Carbon Monoxide Awareness
- 94 Chimneys & Flues
- 2K Domestic Hot Water
- 5.5K Gas Heating
- 101 Geothermal
- 156 Indoor-Air Quality
- 3.5K Oil Heating
- 64 Pipe Deterioration
- 927 Plumbing
- 6.1K Radiant Heating
- 383 Solar
- 15.1K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 48 Job Opportunities
- 17 Recall Announcements