BPI CO Best Practices Standards
I think this needs additional work and appreciate anyones input into this document.
Many thanks to the folks at carbonmonoxidekills.org for allowing us to use it.
ME
  • MikeyB
    MikeyB Member Posts: 696
    Standards
    Hey Mark, I was wondering if you could clear this up for me, maybe im not reading it right , but under the heading "Standards for Action Levels"  the last sentence reads "The action levels are considered net indoor ambient readings, i.e. -indoor ambient minus outdoor ambient readings" So for example if we have a indoor ambient reading in a house of 15 ppm, and we were able to get a reading of 9 ppm in the outside air (before we enter the house) the reading we log down  for our indoor reading would be 6 ppm ambient, which would be a Normal reading for indoor ambient and would require "No Action"  Thanks again Mark
  • Mark Eatherton
    Mark Eatherton Member Posts: 5,874
    That is the way I read it Mike...
    And to be sure, I would write the OSA ambient down for reference, and do the math right there on the paper so there is no confusion.
    BTW, the highest ambient CO I have seen here in the Denver Basin, which is notorious for bad air inversions is 2 ppm.
    I confirmed this thru the Colorado Dept. of Health web site. 1.9 ppm is the max seen last year.
    If you were sampling down stream of a major CO producer (steel mill, coke factory) I suppose you could see higher than that tho...
    Food for thought.
    ME
  • Tim McElwain
    Tim McElwain Member Posts: 4,657
    DO NOT I REPEAT
    DO NOT set your outdoor ambient up near the exhaust from your service van or truck. Do not laugh it happens.
  • Mark Eatherton
    Good point....
    What ever happened to common sense?
    Funny thing. I inadvertently tested my personal CO detector the other day. Had it on my belt, back the Cherokee up to the house to start loading tools for a job, when suddenly, my rattler started rattling. What the? looked down and it was at 40 ppm. Set to begin buzzing at 35 ppm. Guess it works OKay!
    ME
  • MikeyB
    edited March 2010
    Standards
    Great points Tim & Mark, I learn alot from you guys, thanks again for taking the time. Also under Best Practices for Domestic HW Tank CO Testing Draft Testing, they mention normal draft is between .01"WC & .02"WC, should this be written as a negative reading (-) ?
  • Mark Eatherton
    Affirmative....
    it is supposed to be listed as a NEGATIVE. (-). If it is positive, you have a "situation" on your hands.
    ME