Some Questions About Installing a Steam Boiler
Hi, I'm installing a new steam boiler, Williamson GSA 150. System is One-pipe parallel w/ wet return. I have a few questions and looking for advice:
- The manual recommends 2-1/2" pipe for header. My current pipes are 2". Can I use 2" pipe?
- Can you recommend where the best place to put maintenance valves and access fittings?
- Should I install an automatic feeder for water supply? If so, where should that be located?
Thanks,
Steve
I just I stalled the same boiler in my house a few months back. 2in (insulated) single pipe works fine. Top taping is 3in so 3in-to-2in reducer might be $$ (it was in my case).
Install skim taping valve (the boiler doesn't come with the pipes or the valve).
Also replace the bottom drain valve with something better.
Install the "paraphenalia" on the side most convenient to service the boiler.
If you maintain the boiler then is no need to install water feeder (mine is still disconnected).
GSA125 is the same boiler (size, weight and water content) but it has 5 burners instead of 6 = slower steam production = generally better.
Have you measured your radiators yet?
https://www.youtube.com/@HeatingBlog2 -
If the manual says 2.5" pipe use a minimum of 2.5" pipe. It might work ok with smaller pipe in certain installations but you're rolling the dice and you don't want to buy everything twice. the riser(s) to the main(s) can match the size of the main(s) but the risers to the header and the header should be at a minimum the sizes specified in the manual. The additional cross sectional area allows the steam to slow down and any entrained water to settle out. This is especially important when the boiler is new and you are skimming off the oils from the boiler and new piping, the proper header will make it misbehave less in between skimmings until you get all the oil out.
7 -
The system seemed to work fine with 2" pipe with the previous boiler that was larger, a Crown BSI 172.
@patrykrebisz thanks for your advice on installing a skimming valve. I started watching your videos. I'll be watching the one about pressuretrol again soon. The GSA 125 is a bit too small for my system. I did measure the radiators and the 150 was the minimum size.
@mattmia2 thanks for your insight on the cross sectional area. Yeah, I guess I can pipe the riser to the header at 2.5" and tee off at 2" to the riser to the main. The reason I ask the question about size is because the manual doesn't explicitly specify 2.5". It says it recommends it.
that is a weil mclain with a different badge. pretty sure they specify minimum sizes for the header, risers, and equalizer.
Use the recommended pipe sizes or larger. It's a different boiler, it may behave differently. Also it is new and not a crusty old boiler that its efficiency may have diminished over the years. If something does not work correctly you don't want the fingers pointing at the installer which is you.
One Pipe System0 -
You should be able to easily flush out the wet return and the boiler. Without pushing any wet return crud into the boiler. Skimming should be easy also.
One Pipe System0 -
After servicing lots of steam boilers and seeing some questionable installs over the years I see that contractors default to 2" pipe. The reason you might ask is this 2" is easier to thread and requires no additional threading equipment. 21/2" pipe on up requires an expensive gear reduction threader. Most hardware stores and big box stores that thread pipe don't have them either.
While 2" may work with an old boiler a new boiler is going to react differently. Avoid the frustration and headache. Bump up the pipe size. With a little planning you can order 21/2 fittings and have it threaded.
Owner of Grunaire Climate Solutions. Check us out under the locate a contractor section. Located in Detroit area.
1 -
I agree 100%, but out of curiosity could you use 2” if you used both outlets
The answer is you should use the manufacturer recommended sizes. However, they are very conservatively engineered and we see over and over cases where smaller (or fewer) pipes are fine.
I have been experimentally running my 63-03L with a single 1-1/4" pipe directly from the boiler to the main without even a header or an equalizer since last winter without issue.
The idea of slowing down the steam to allow entrained water droplets to fall out is mythological. The droplets fall out regardless.
Here's my video which is too long but feel free to click through it:
I agree we have all seen boilers they are piped all wrong and you can stand in front of it and stare at it in disbelief and say it will not work but it does.
Yours works but you are meticulous with maintenance and water quality.
I have always felt that drop headers and going over and above the mfg recommendations is a waste of $$$$. I just take a middle of the road approach and just pipe it to the MFG minimum spec. As a former contractor if you don't do that and have problems going back it to make changes and fooling with it is not worth the risk.
JMHO
The difference in the diameter between 2" and 2 1/2" is only 1/2" but the area difference is 1.56 x a 2" pipe equals a 2 1/2" pipe.
2 -
I agree, I have quite a few steam boilers that are installed completely wrong but they've been there for 75 years now and the building heats just fine everybody's happy and the water level doesn't bounce. One thing to look for is that the steam velocity isn't too high. At that size your velocity is about 41fps. Recommended is 25ish if i remember right.
Owner
Steamnowrockford.com
I'd like to see any evidence that "steam velocity" is even a thing of concern. I never have seen it, and I've looked. I'm VERY willing to see it if anyone can show it.
When I took my outlet from my boiler down to 5/8" (yes, 5/8"), the problem wasn't anything with the steam velocity.
That is, not in the sense you are thinking of.
The steam velocity exiting the boiler was dramatically slowed, in fact, because it couldn't squeeze through the 5/8" pipe quickly enough. It caused the steam to seek another path, through the equalizer to the header.
If there hadn't been the equalizer path, the boiler would have just shut down from the pressuretrol.
I will assert that the idea that the steam velocity carries liquid water out of the boiler is false in residential boilers. The velocity in the steam chest is reduced for the reason I said above…which actually reduces the chance of "entrained water" exiting the boiler.
boilers before the early 70's or so had more area above the water that did a lot of the separation that modern boilers have to do with the header so older boilers don't so much need the header setup that modern boilers need.
Side outlet boilers have a lot less separation between the exiting steam and the water so the header is more important in those.
@ethicalpaul's setup without an equalizer could also push the water out of the boiler in to the returns depending on where the return piping is and pressuretrol settings.
1 -
Interesting. Maybe it's more accurate to say the velocity in the risers is a concern. Having low velocity there will reduce any kind of bernoulli effect from higher velocity.
Where did you size it down? The riser or header?
Owner
But I have seen that modern boilers don't need it.
Theoretically this makes sense, but I haven't seen this either. My old boiler was a side-outlet Utica and it had a ridiculously bad near-boiler-piping and I was able to get it working fine with not nearly the knowledge that I have today.=
No, it can't because the main is the "equalizer" that delivers the same pressure to the end of the main that exists at the boiler. You still haven't watched my video about that? /cry
No, I don't think the velocity in the risers is a concern at all. If the risers are undersized. Yes, the velocity there will be a little higher. But it will be slower in the steam chamber at the top of the boiler. There's no bernoulli effect that seems to matter, and any droplets that do get into the steam do not stay in it. They hit the walls of the pipe and become a film there that either runs back to the boiler, or flows down the main, or gets re-evaporated by the steam passing by.
I put smaller pipes from the top of the boiler to the header, and then I went insane and ran a smaller pipe from the boiler straight to the main, removing the header and equalizer completely which caused the boiler to…work normally.
See my sight glass boiler videos: https://bit.ly/3sZW1el0
- 135 Chimneys & Flues
- 16.2K Strictly Steam