GVD‑6 damper microswitch issues
Just installed a new boiler and the damper is giving me issue.
I have it set to Keep Open. After call for heat ends, i hear the motor working even though the damper is set to keep open and thus not rotating. It only stops to make noize when i turn the shaft slightly to the left to engage the microswitch internally. I presume i just have to twist some tab inside so it engages the switch. Am i correct?
»»» See my steam heat YouTube videos:
https://www.youtube.com/@HeatingBlog
Comments
-
Nope. The motor assembly is bad. Have it replaced under warranty.
1 -
Under warranty is the best time to get the part changed. If the installer is you, then get the new damper from the boiler manufacturer through your supplier.
If you are the homeowner, call the contractor. If he is someone who stands behind his work, he should not charge you any labor for that repair as long as it has not been more than a year since the installation was completed.
Edward Young Retired
After you make that expensive repair and you still have the same problem, What will you check next?
0 -
How is the motor bad if it opens and closes?
Just curious before i open it up and look for "answers."
»»» See my steam heat YouTube videos:
https://www.youtube.com/@HeatingBlog0 -
" i hear the motor working even though the damper is not rotating "
That sounds like a mechanical issue not a microswitch issue.
I agree with above, if its under warranty go that route.
National - U.S. Gas Boiler 45+ Years Old
Steam 300 SQ. FT. - EDR 347
One Pipe System0 -
Ok i fixed the original info i was sharing. The side switch is turned to Keep Open setting. After call for heat ends, it seems the microswitch mechanically disengages and thus the motor tries to work (hear it spinning) but nothing happens. The damper stays open. The motor tries to rotate until i manually push the damper by fraction of a millimeter to re engage the micro switch.
»»» See my steam heat YouTube videos:
https://www.youtube.com/@HeatingBlog0 -
if that is in Warranty stop messing with it and replace it.
break something and you’ll loose the warranty.0 -
Oh you Americans love your warranties… I take things apart. This is $50 motor. Even if i breaks something i'll learn how it works.
»»» See my steam heat YouTube videos:
https://www.youtube.com/@HeatingBlog0 -
Here is the replacement motor unit:
https://www.supplyhouse.com/Field-Controls-70009800-GVD-Vent-Damper-Motor-Assembly-Metal-BaseYou need to be very careful with this. If the boiler fires up with the damper closed, exhaust gases will escape into the boiler room. This could contain carbon monoxide, which can kill you.
0 -
I would hope any boiler equipped with a damper is also equipped with a spill switch.
Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.
0 -
There are more parts inside that black plastic housing than just the motor. Actually, the motor itself is probably just fine.
The way that assembly is made, there are no serviceable parts inside that black plastic cover. You can’t get a new shaft to replace a bent shaft or a new microswitch to replace one that is not closing.
The part that is bad inside that motor housing is not something the vent damper manufacturer wants you to “adjust” or “service.” The manufacturer will, however, usually provide a complete motor assembly with all of the other parts inside it, or perhaps a complete damper assembly, under warranty at no charge.
Once you "open that up to look for answers", you may void the warranty.
But it is your toy to play with. do what you want with it.
Signed: Ed
with over 40 years experience
Edward Young Retired
After you make that expensive repair and you still have the same problem, What will you check next?
0
Categories
- All Categories
- 87.8K THE MAIN WALL
- 3.3K A-C, Heat Pumps & Refrigeration
- 59 Biomass
- 430 Carbon Monoxide Awareness
- 130 Chimneys & Flues
- 2.2K Domestic Hot Water
- 6K Gas Heating
- 124 Geothermal
- 170 Indoor-Air Quality
- 3.8K Oil Heating
- 79 Pipe Deterioration
- 1.1K Plumbing
- 6.7K Radiant Heating
- 396 Solar
- 16.1K Strictly Steam
- 3.5K Thermostats and Controls
- 56 Water Quality
- 51 Industry Classes
- 51 Job Opportunities
- 18 Recall Announcements