Replacing near boiler supply pipes/valves

Options
guzzinerd
guzzinerd Member Posts: 463
edited August 10 in Strictly Steam

The valves on this loop are in pretty rough shape and have scheduled a plumber to come in and replace them this week:

7225.jpg

My question is on the procedure. Is this correct?

1. drain the boiler

2.replace the valves/pipes

3. refill and then fire the boiler to rid of the oxygen

.. or is there a way to not lose the boiler water while replacing those valves?

Thanks

Alex

P.s. just a reminder that I'm in remote new mexico mountains, no steam people nearby

Bryant 245-8, 430k btu, 2-pipe steam in a 1930s 6-unit 1-story apt building in the NM mountains. 26 radiators 3800sqf

7225.jpg 289.2K

Comments

  • mattmia2
    mattmia2 Member Posts: 17,831

    depends on how much of an issue refilling it is. you could probably do some things with some jet sweats or plugs to remove things and plug them and only lose a couple gallons but that is more trouble than its worth unless refilling it is difficult.

  • Jamie Hall
    Jamie Hall Member Posts: 27,669

    Steam? Check the water level in the boiler — and lower it just enough to be below those valves. Then shut off the supply and have at it. May I suggest quarter turn ball valves for replacement?

    Br. Jamie, osb
    Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England
    PC7060
  • EBEBRATT-Ed
    EBEBRATT-Ed Member Posts: 20,765

    Your going to have to drain the whole boiler. just drain it and refill when done. Run the burner until it steams and then shut it down.

    guzzinerd
  • guzzinerd
    guzzinerd Member Posts: 463

    Yes, steam. I had a new ball valve replacement, strainer kit and gaskets ready but the thing is a real mess on the inside. Then i found a receipt from the last ball valve replacement dated July of 2005 so I just ordered a new unit from Patriot.

    Bryant 245-8, 430k btu, 2-pipe steam in a 1930s 6-unit 1-story apt building in the NM mountains. 26 radiators 3800sqf